I had the same fault on the same model UPS is there any one have information how to solve this problem
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:12 PM . Last Modified: 2024-03-06 11:20 PM
You will have to either replace the battery pack/s or take them out and charge them. They are probably dead if left to stand for 5 months but some smart chargers can revive the individual 12v batteries.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:12 PM . Last Modified: 2024-03-06 11:20 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:12 PM . Last Modified: 2024-03-06 11:20 PM
I had the same fault on the same model UPS is there any one have information how to solve this problem
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:12 PM . Last Modified: 2024-03-06 11:20 PM
You will have to either replace the battery pack/s or take them out and charge them. They are probably dead if left to stand for 5 months but some smart chargers can revive the individual 12v batteries.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-14 09:50 PM
I have some fault for the UPS SRT3000XLI, after backup time about 3 hours until UPS shutdown and when AC input restore why it doesn't auto restart.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-18 09:25 AM
There could be several reasons why a UPS may not come back online after the AC is restored.
1. on the webpage under configuration > shutdown under the section titled "PowerChute Shutdown Parameters" make sure that "Restart when power is restored" radio button is checked
2. The power to the UPS may not be in the proper frequency of missing a ground.
3. One or more of the batteries has gone bad
If you have the alert above then you have a bad battery. UPSs generally will not come on if they do not see AC and battery power.