Upgraded MGE Comets with Symmetra PY80, now outgrowing it and looking for clarity on the Galaxy Line

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Upgraded MGE Comets with Symmetra PY80, now outgrowing it and looking for clarity on the Galaxy Line
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:47 AM . Last Modified: ‎2024-03-19 01:51 AM

0 Likes
6
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:47 AM . Last Modified: ‎2024-03-19 01:51 AM

Upgraded MGE Comets with Symmetra PY80, now outgrowing it and looking for clarity on the Galaxy Line

We operate a data-center and fiber transport/Co0Lo facility here in Evansville Indiana.   We upgraded to a Symmetra PY80 from a pair of MGE Comets about 4 years ago.  We are now outgrowing the PY80.  We have been looking at the Galaxy PW-150/180 product.  Back when we were looking at the PY80, there was LOTS of engineering data readily available, as well as systems/features comparisons of products across the lines.  Now the website seems cryptic and links to resources described/discussed in the forums are all broken.

We liked the modularity/upgradeability of the Symmetra PY-series, as we started at 50kW and have added modules and batteries to the point we are maxing out, the information on the Galaxy suggests we won't have that ability.

Can someone give me clarity?

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

Hi David,

Bill made me aware of your situation as I manage the relationships with many of the colocation and managed service providers in the eastern US. Matter of fact I sat down with Tom Kolb of your firm a couple years ago

Yes I am a sales person but I get your comment loud and clear that you are not looking to purchase new equipment just seeking information on Schneider gear

I am teamed with a systems engineer who could answer any and all of your questions

I assure you that no attempt will be made to sell you anything, we are here to assist. 

I understand Bill is doing his job but from my perspective I really don't need the SN of your current unit unless we really get into the weeds on this

Please contact me at tim.shackelford@schneider-electric.com or call 314-570-6370 and we can get your questions answered

Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

Hi,

Sorry for the inconvenience. Would you mind sharing the serial number of the Symmetra? Once I have that information I will look up your account and will be able to have the proper person contact you to assist you with your research. 

Again, sorry for the inconvenience with the site. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

We aren't buying new from a dealer, is that relevant to discussion?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

Hi,

Yes. It is relevant to help me assist you. I can point you to the web but you have already said you don't care for that approach. If I have your account information I can look up to see who is assigned to you and they will help with the needed research saving you time. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

I don't mind sharing the SN as much as I don't want a sales person selling/talking to me, I want an engineer sharing system architecture and operating characteristics.  We are not looking to engage your sales for a new system, and if this forum is just a bridge to that resource then I have made a mistake...   Bad information from "sales engineers" can be a resume changing experience when something goes wrong...

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

0 Likes
0
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

Hi,

You would work with a team of people that yes include sales but also systems architects, and systems integrators. They will review what equipment you now have and ask questions about what you anticipate for the near, long term future, and review your infrastructure. A recommendation would be made only after a through review.   

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:48 AM . Last Modified: ‎2024-03-19 01:51 AM

Hi David,

Bill made me aware of your situation as I manage the relationships with many of the colocation and managed service providers in the eastern US. Matter of fact I sat down with Tom Kolb of your firm a couple years ago

Yes I am a sales person but I get your comment loud and clear that you are not looking to purchase new equipment just seeking information on Schneider gear

I am teamed with a systems engineer who could answer any and all of your questions

I assure you that no attempt will be made to sell you anything, we are here to assist. 

I understand Bill is doing his job but from my perspective I really don't need the SN of your current unit unless we really get into the weeds on this

Please contact me at tim.shackelford@schneider-electric.com or call 314-570-6370 and we can get your questions answered

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore