Understanding PDU's

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Understanding PDU's
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

0 Likes
4
1375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

Understanding PDU's

Hi Guys,

I'm trying to get a better understanding of how the power is measured across PDU's and phases, so that we can better plan our kit installs. We run a data centre that is kind of a halfway house between Colo and owned in that we rent a DC room, but we have a free hand to use it as we see fit. We currently have 3 "pairs" of main PDU's, all are rated at 250A. How does that equate to what's loaded on the 3 phases. ie if each phase were to register an average current of say 80A, would that indicate that we're running close to the 250A limit ?? or does it not work like that ?? What would be sensible limit to put on each phase ??

Thanks,
Mark.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • pdu
  • phases
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

Hi,

Knowing that your (3) PDU's are each rated at 250amps implies that you actually have 250 amps on each phase. So if you are running ~80 amps on each phase, you would only be using ~1/3 of your total available power. As far as a sensible limit, 80% is always a nice rule of thumb, so 200 amps per phase. You certainly can take things much closer to the 250 amp limit, but once you get above 80% you should start to consider whether you need to expand. Also, for any 3-Phase power, try and keep the load on your 3 phases as balanced as possible (because if any one leg went over 250 amps, it would trip the entire circuit).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

Hello Mark ,

I agree that a 250 amp feed is sizeable, but not out side the range of common 3-Phase equipment. As a standard, when dealing with 3-phase equipment, current limits are listed per phase. Could you take a look at the breaker that feeds any of these PDU's. If the breaker says 250 amps, then it would be 250 amps per phase.
to relate this to some APC equipment:
a 40K PDU requires 175 input protection (208V 3-Phase 175 amp {per phase} Breaker)
60K 225 amp Breaker
80K 350 amp Breaker

Do you have any specific information on the PDU(s) in question. Are they APC or MGE equipment? Perhaps you could locate a model or serial number on one of the PDU's. Also, do you see any KW or KVA ratings? Unlike current ratings, power ratings in kilowatts are always listed as a total, covering all 3 phases.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

No quite true. As I said there are 3 "pairs", each pair having an A feed, and a B feed for resilliency ( but separate PDU's ). The fact that there are 3 pairs is maybe a little misleading, and I think, just pure coincidence. Each PDU of each pair is rated at 250A. Now to me, 250A on each phase seem pretty hefty. Which is why I 'm questioning it. Is there anything I can look for that will tell me whether its per phase or overall ??

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

Here is a owners manual for the MGE brand PDU's the outputs of these PDU's can be as high as ~800A per phase for the 300kva pdu's.

http://www.apcmedia.com/salestools/MBPN-7SPHE4_R0_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

0 Likes
0
1375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:09 AM . Last Modified: ‎2024-03-18 03:46 AM

Hi,

Knowing that your (3) PDU's are each rated at 250amps implies that you actually have 250 amps on each phase. So if you are running ~80 amps on each phase, you would only be using ~1/3 of your total available power. As far as a sensible limit, 80% is always a nice rule of thumb, so 200 amps per phase. You certainly can take things much closer to the 250 amp limit, but once you get above 80% you should start to consider whether you need to expand. Also, for any 3-Phase power, try and keep the load on your 3 phases as balanced as possible (because if any one leg went over 250 amps, it would trip the entire circuit).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login