Unathorized SNMP Alerts

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
Enter a search word
    Turn off suggestions

    Didn't find what you were looking for? Explore advanced search

    Enter a search word
      Turn off suggestions

      Didn't find what you were looking for? Explore advanced search

      Enter a user name or rank
        Turn off suggestions

        Didn't find what you were looking for? Explore advanced search

        Enter a search word
          Turn off suggestions

          Didn't find what you were looking for? Explore advanced search

          Enter a search word
            Turn off suggestions

            Didn't find what you were looking for? Explore advanced search

            cancel
            Turn on suggestions
            Showing results for 
            Show  only  | Search instead for 
            Did you mean: 
            Important Note
            • Home
            • Schneider Electric Community
            • APC UPS, Critical Power, Cooling and Racks
            • APC UPS Data Center & Enterprise Solutions Forum
            • Re: Unathorized SNMP Alerts
            Options
            • Mark Topic as New
            • Mark Topic as Read
            • Float this Topic for Current User
            • Bookmark
            • Subscribe
            • Mute
            • Printer Friendly Page
            Invite a Co-worker
            Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
            You have entered an invalid email address. Please re-enter the email address.
            This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
            Please enter email address
            Send Invite Cancel
            Invitation Sent
            Your invitation was sent.Thanks for sharing Exchange with your co-worker.
            Send New Invite Close
            Top Experts
            User Count
            BillP
            Administrator BillP Administrator
            5060
            voidstar_apc
            Janeway voidstar_apc
            196
            Teken
            Spock Teken
            136
            Erasmus_apc
            Sisko Erasmus_apc
            112
            View All

            Free

            English

            Data Center Certified Associate Exam Development Path

            Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

            4.0
            Register Browse SE University

            Invite a Colleague

            Found this content useful? Share it with a Colleague!

            Invite a Colleague Invite
            Solved Go to Solution
            Back to APC UPS Data Center & Enterprise Solutions Forum
            Start a Topic
            Solved
            Anonymous user
            Not applicable

            Posted: ‎2021-06-29 10:51 PM . Last Modified: ‎2024-03-12 01:06 AM

            0 Likes
            9
            7762
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:51 PM . Last Modified: ‎2024-03-12 01:06 AM

            Unathorized SNMP Alerts

            For the last 2 or 3 weeks, I have several UPSs at various locations that are getting bombarded with SNMP requests from various user workstations. I can't find any commonality with them, some are windows 7 and others are Windows 10. The messages seem to be showing up when people turn on or restart their computers.

             We've performed malware and anti-virus scans on everything and all comes back clean. Has anybody seen anything like this or have any ideas? I'm tired of my email blowing up with these alerts.

            Labels
            • Labels:
            • UPS Management Devices & PowerChute Software
            Reply

            Link copied. Please paste this link to share this article on your social media post.

            • All forum topics
            • Previous Topic
            • Next Topic

            Accepted Solutions
            Anonymous user
            Not applicable

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            0 Likes
            0
            7762
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            Sorry to necro an old thread but I also experienced this. It was the Konica Minolta Device Agent on a Windows server performing SNMP probes. Stopped and disabled the service.

            See Answer In Context

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Replies 9
            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-29 10:51 PM . Last Modified: ‎2024-03-12 01:06 AM

            0 Likes
            0
            7762
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:51 PM . Last Modified: ‎2024-03-12 01:06 AM

            Hi Ryan,

            Are you actually using SNMP with the Network Management Cards installed in the UPS (these are what send the alerts)? If not, we can disable SNMP completely.

            SNMPv1 is enabled by default and SNMPv3 can also be enabled. Which one are you using? (Side note: Only in AOS v6.4.6 and higher did we start logging this for SNMPv3 attempts. Prior to that, only v1 attempts were logged.)

            In general, it would seem like there is some sort of SNMP Agent on the user's computer's potentially assuming the IP address doing the attempt is logged in the message and you've pinpointed it to user's machines. We can look at changing the SNMP credentials and access control on the UPSs (specifically the network management card) or may have to dig further on the user's machines to see what is installed there. 

            I have never seen this be the cause of the Network Management Card besides some incorrect credentials or settings.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Anonymous user
            Not applicable

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            0 Likes
            0
            7762
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            I'm having the same problem and not finding any solutions online. Random computers and servers in the network seem to be trying to access the UPS GUI. Below is the email alert I get.

            Name :

            Location : F

            Contact  : J

            http://

            http://

            http:// (Local) http://

            Serial Number : 5A1xxxxxxxxx

            Device Serial Number : AS1xxxxxxxxx

            Date : 10/26/2017

            Time : 07:17:15

            Code : 0x0004

            Informational - Detected an unauthorized user attempting to access the SNMP interface from X.X.X.X

            Please let us know what to do about these alerts. Other department heads get these reports to let them know when we lose power, and these reports are causing panic.

            Thank you,

            Jason

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            0 Likes
            0
            7762
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            Hi Jason - are you using SNMP for monitoring? If you're not using it for monitoring, then you can completely disable both the SNMPv1 and SNMPv3 interfaces on the Network Management Card in the UPS. SNMPv1 is enabled by default. 

            If you're using SNMP monitoring, then you can at least evaluate what the SNMP access controls are set to now and see if you can adjust them accordingly. 

            Depending on the situation too, you can also consider specifically disabling these specific events for notifications from email. This of course wouldn't address the root of the problem and you'll still see these messages from the event log (but we usually don't recommend disabling from the event log itself but it can be done).

            I am not sure what would work best for either of you. Instructions on the above options depend on which firmware version(s) you may have. If you can share those, then we can try to provide you some guidance on changing the settings if you need it.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Anonymous user
            Not applicable

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            0 Likes
            0
            7762
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            I can try that, but I'm wondering what changed to make this reporting go haywire all of a sudden?

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            0 Likes
            0
            7762
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            Hi Jason - Did you recently upgrade the network management card firmware by chance? If you are using SNMPv3, I can say that these messages would've only started being logged as of v6.4.6 AOS (APC Operating System). So, previously they may have gone unnoticed or there was no visibility into them. This would only be a possible cause if using SNMPv3 specifically and you have v6.4.6.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            0 Likes
            0
            7762
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            I came across this post while I was researching a problem that I am having and I am hoping someone can help.
            About 3 weeks ago I started to receive the following e-mails from my Smart1500 USP;
            “Detected an unauthorized user attempting to access the SNMP interface from 192.168.xxx.xx”.
            We are using SNMP for monitoring and only SNMPv1 is enabled, also the community on the UPS and workstations match. I receive the e-mails 3 times a week. Each attempt comes from one of 3 different workstations on our network. According to the e-mails each workstation attempts the access once each week on the same day, one on Friday, one on Saturday and one on Tuesday. The only thing these workstations have in common is that they are all running Windows 7. One of the workstations is a new computer right out of the box. After I started to receive the e-mails I contacted  APC support team a couple of times, in doing so we have confirmed that SNMP is configured correctly on the UPS, we have upgraded the firmware on the UPS in hopes that the e-mails would stop and they showed me how to disable the e-mails. However, I still do not know what is causing the issue. The UPS has been in service for years and with the exception of the one workstation the other two computer have been up and running now for 1 to 2 years. I have run multiple virus scans on the computers and they always come up clean. APC support stated that they cannot help with the workstations. Can someone please give me an idea as to what could be running on these workstations that would cause this problem?
            Reply

            Link copied. Please paste this link to share this article on your social media post.

            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            0 Likes
            0
            7762
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            If they always happen on the same PCs at a certain time of the day, I was thinking can you rig up a packet capture with Wireshark or similar tool to see if you can capture the requests happening over the network? I am not sure if it happens in the middle of the night or what.

            It is really hard to answer this without seeing what is installed specifically. You could evaluate what services and processes are running on the PC at the time and research if any of them support SNMP polling. 

            Do these tools run any network penetration or scanning software which may scan a certain network or subnet periodically? Or any SNMP MIB browsers perhaps? (I use MIB browsers to test certain OIDs and I wouldn't expect them to scan devices unless I specify a certain IP). Those may be something obvious you already checked but I don't know if a host intrusion detection program too, which often comes as part of a virus scanner package may be the culprit.

            Other than that I am not aware of any common culprits of this we've found with other customers or anything unfortunately.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            cs_support_apc
            cs_support_apc
            Cadet

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            0 Likes
            0
            7762
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            Replying to this old thread so others can reference...

            I had this issue and discovered it was the Canon network scanning selector utility for my home printer that was the culprit.

            I suspect other manufacturer's utilities for network printer or scanner discovery may cause the same effect.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Anonymous user
            Not applicable

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            0 Likes
            0
            7763
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-29 10:52 PM . Last Modified: ‎2024-03-12 01:05 AM

            Sorry to necro an old thread but I also experienced this. It was the Konica Minolta Device Agent on a Windows server performing SNMP probes. Stopped and disabled the service.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Preview Exit Preview

            li.media.uploader-dialog.title

            • li.media.uploader-dialog.tabs.upload li.media.uploader-dialog.tabs.upload
            • li.media.uploader-dialog.tabs.web li.media.uploader-dialog.tabs.web
            • li.media.uploader-dialog.tabs.saved li.media.uploader-dialog.tabs.saved
            li.media.album-selector.label
            • li.media.album-selector.title
            • li.media.album-selector.new.title
            • li.media.album-selector.label
              • li.media.album-selector.title
              • li.media.album-selector.new.title
              li.media.image-upload.drag
              li.media.image-upload.drop
              li.media.image-upload.mobile.instruction
              li.media.image-upload.no-flash
            li.media.uploader-dialog.title

            never-displayed

            You must be signed in to add attachments

            never-displayed

             

            You’ve reached the end of your document

            WHAT’S NEXT?

            Ask our Experts

            Didn't find what you are looking for? Ask our experts!

            My Dashboard

            Check out the new Feeds and activities that are relevant to you.

            To The Top!

            Forums

            • APC UPS Data Center Backup Solutions
            • EcoStruxure IT
            • EcoStruxure Geo SCADA Expert
            • Metering & Power Quality
            • Schneider Electric Wiser

            Knowledge Center

            Events & webinars

            Ideas

            Blogs

            Get Started

            • Ask the Community
            • Community Guidelines
            • Community User Guide
            • How-To & Best Practice
            • Experts Leaderboard
            • Contact Support
            Brand-Logo
            Welcome to Schneider Electric Community!
            Forum-Icon

            You have two options to continue your visit.

            LOGIN / Register

            Why logging in?
            • You enable the complete set of features available, such as posting, sharing, subscribing, private messaging and more.
            • You unlock the access to the whole content that Schneider Electric Community has to offer, including the gated items and the special events.
            And it’s free of charge!!!

            OR

            Continue as a guest

            Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

            Welcome!

            Welcome to your new personalized space.

            of 1

            Explore
            Translating the page…
            The page is currently translating. Please wait.
            Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.