Posted: 2022-09-22 01:32 AM
I know this has been asked before elsewhere a while ago, but it seems to still be an issue.
If I uncheck "Skip outlet off delay" and click "Apply", then go back to the outlet settings, it's checked again.
Smart-UPS SRT 2200
AP9641 NMC with firmware v2.2.1.1 (was v1.6)
Updating firmware to the latest didn't affect the issue. Is this setting only valid if one of the load shedding settings is enabled or is it a global setting? In my testing with the earlier firmware, this being checked didn't seem to affect power off delay.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-22 05:54 AM
Are you using load shedding and are you using PowerChute? If you are not using load shedding the "skip outlet off delay" has no effect on the UPS behavior.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-22 06:03 AM
Thanks for confirming. I'm not using load shedding. I'm using PowerChute Network Shutdown VM Appliance with VMware hosts.