Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-07-09 04:12 AM . Last Modified: 2024-02-14 11:08 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:12 AM . Last Modified: 2024-02-14 11:08 PM
Hi,
We have APC PDU 7941. I tried to login through console with apc/apc username/password but it is not working. When I tried to reset the password through reset button it is also not working. I am able to login with other username device using password apc.
Can someone advise how I can reset the password or what is the default username or password for administrator user.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:12 AM . Last Modified: 2024-02-14 11:08 PM
The default user name/password is apc/apc as you already seemed to try.
The only way to reset the administrator password is by using a special timing sequence while serially connected and the pinhole reset button on the PDU display, as mentioned here -> http://www.schneider-electric.us/en/faqs/FA156075 (refer to NMC1 instructions)
You'll want to make sure the pinhole reset button is actually making constant. Your post seemed inferred maybe the reset button wasn't working but I can't tell if you meant the process or the physical button. Verify when you press the button during the procedure that the LEDs react as noted.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:12 AM . Last Modified: 2024-02-14 11:08 PM
The default user name/password is apc/apc as you already seemed to try.
The only way to reset the administrator password is by using a special timing sequence while serially connected and the pinhole reset button on the PDU display, as mentioned here -> http://www.schneider-electric.us/en/faqs/FA156075 (refer to NMC1 instructions)
You'll want to make sure the pinhole reset button is actually making constant. Your post seemed inferred maybe the reset button wasn't working but I can't tell if you meant the process or the physical button. Verify when you press the button during the procedure that the LEDs react as noted.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
You have two options to continue your visit.
OR