AP7723 Automatic Transfer Switch Chassis Earth Bond - yes or no?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7723 Automatic Transfer Switch Chassis Earth Bond - yes or no?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:08 PM

0 Likes
4
1543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:08 PM

AP7723 Automatic Transfer Switch Chassis Earth Bond - yes or no?

I recently suffered a destroyed AP7723 ATS and UPS (SURT2000) during commissioning/testing. The defect occurred having just added the ATS to an existing UPS system whilst manually switching between 2 x UPS input supplies (2 x SURT2000) whilst on load (approx 1100W). The UPS generated an 'over-voltage' error and is now stuck in permanent bypass mode. Trouble is, I don't know if the ATS destroyed the UPS or the other way-round. 

Having replaced both the UPS and APS, I then attached an earth bond to the chassis of the ATS. I then continually repeated the ATS input selection testing and the install worked seamlessly as designed.

I have no idea if I was just unlucky with the first failure, or if the addition of an earth bond made any difference in terms of voltage suppression during switch-over. 

I assume the previous earth path was only via the 2 x UPS inputs, so I have no idea how these are referenced to each other - or to chassis ground. The brief ATS instructions refer to fitting an earth bond if fault current is unknown (or greater than a certain figure) but could the lack of earth-bond have contributed to the original failure?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap7723
  • ats
  • automatic
  • bond
  • chassis
  • earth
  • switch
  • transfer
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:07 PM

0 Likes
0
1541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:07 PM

Hi Bill,

I've checked the faulty ATS again and can confirm that the Source A 24V PSU is dead i.e. reading 0V via serial or Ethernet with an input supply present. You can hear a relay 'click' when the lead is inserted into Source A, but you have to power the unit up via Source B.

I've attached a text version of the log file, which shows many 'over frequency violation Source A' errors. In this case, both sources were from SURT2K UPS' - albeit the one feeding Source A failed simultaneously to the ATS input failure.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:08 PM

0 Likes
0
1541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:08 PM

Hi,

The ATS would be using the ground of the source (the UPS in the first case) - did you do any configuration to the ATS before deploying it? Is it possible to send us the configuration files/event logs/event counts of the ATS?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:08 PM

0 Likes
0
1541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:08 PM

Hi Bill. The only thing I did prior to fitment was upgrade the firmware to 3.9.0, select 'no source preference' and lock-out the front panel button. No other parameters were changed.

  • Tags:
  • ap7723
  • ats
  • auto
  • switch
  • transfer
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:08 PM

0 Likes
0
1541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:08 PM

Hi,

Without the logs it is difficult to say what may have caused the issue. As mentioned earlier the ATS should have been grounded while plugged into a UPS assuming the UPS was grounded. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:07 PM

0 Likes
0
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:12 AM . Last Modified: ‎2024-02-14 11:07 PM

Hi Bill,

I've checked the faulty ATS again and can confirm that the Source A 24V PSU is dead i.e. reading 0V via serial or Ethernet with an input supply present. You can hear a relay 'click' when the lead is inserted into Source A, but you have to power the unit up via Source B.

I've attached a text version of the log file, which shows many 'over frequency violation Source A' errors. In this case, both sources were from SURT2K UPS' - albeit the one feeding Source A failed simultaneously to the ATS input failure.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of