Hi again,
I am trying to connect with an AP7960 so that I can reset the IP on it.
I am using a Lenovo ThinkPad T420, Win7 Enterprise SP1, with a USB to serial cable connected to the serial to RJ-11 plug. I have tried connecting via Putty at every possible baud rate, but I still just get a blank (black) Putty screen.
I have also tried plugging it directly into the APC switch that is connected to my ISX manager. I get a link light but no data transfer. So I assume that DHCP can't grab a hold of it. Can someone please point me in the right direction?
Thanks
-Mike
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:07 AM . Last Modified: 2024-03-18 12:06 AM
Nevermind, turns out I had flowcontrol set to "on/off" instead of "none" problem solved.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:07 AM . Last Modified: 2024-03-18 12:06 AM
Nevermind, turns out I had flowcontrol set to "on/off" instead of "none" problem solved.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.