SMT1500 - battery drop when switching to backup

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT1500 - battery drop when switching to backup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
20
2967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

SMT1500 - battery drop when switching to backup

Sorry if this has been asked before, I couldn't find a thread on it.

On my UPS the battery will read 100% whilst it is plugged in to mains - but as soon as it is unplugged the battery will then read 55-65%. Is this normal behaviour?

Cheers,

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

Hi,

What is the load on the UPS while testing? It is possible that the batteries will discharge quickly with a heave load but not normal behavior to drop 40% in seconds. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 20
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

Hi,

That is not normal behaviour. How old is the battery pack and how old is the SMT? If the battery pack is more than 3 years old you should replace it. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

Batteries are new, fitted to a second hand UPS. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

Hi,

What is the load on the UPS while testing? It is possible that the batteries will discharge quickly with a heave load but not normal behavior to drop 40% in seconds. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

Hey, so a load of maybe 4-600w, likely on the lower end of that. 

I do suspect however that it has something to do with load, at the moment I have a very small load (under 1%) and the same problem does not happen .

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

My SMT did this, when I checked the voltage it read 5 volts out so it wasn't charging properly, had to replace it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

Cheers Gareth, how/where do I check the voltage? 

Cheers, 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:06 AM

Ideally with the covers off but on my smt2200i I could take a reading off the front battery packs and times it by 2 (you wouldn't have to times it by 2 on the 1500)

If you can't get probes into the battery plug you will need to take the covers off at your own risk remembering how much of it could kill you if you touched anything!

Compare the readings to the display values and work out the drift.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:06 AM

Cheers Gareth,

I think I should be able to take a reading from the battery connection so I will give that a go before running it with its top off - I am roughly aware of the kind of current build up that must go on inside a UPS so shall have my sensible hat on should I have to run it without the top.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:06 AM

Hi Gareth, 

Had a look at this today and with the unit plugged in my multimeter reads 27.69v. When unplugged the multimeter slowly drops quite quickly at first then slows down to about 25v. Dropping much more slowly after this point.

What display values should i be looking at and how do I work out drift. Sorry for the questions, trying to figure out of it needs to go back (it was cheap) or if it's fixable. 

Edit: should also mention the battery is showing 50%ish at the moment with no drop observed (but with no load). I will test again when it is at 100% with load. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:06 AM

Compare the multimeter reading to the readout the UPS gives for the battery voltage, if it varies that is your drift.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

Thanks Gareth, 

So on mains the unit reads 27.3 and the multimeter 27.62. 

Similar drift when on battery. 25.6 on the multimeter 25.2 on the ups. 

I had left the unit charging as it was on roughly 50%. After just a few hours the unit read 100% charged, this seemed a little odd as lead acid takes time to charge. In any case I then left the unit unplugged before testing it again and when I then plugged it back in it was back down to reading around 50%. 

So something is definitely up here. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

Just grabbed a quick video demonstrating what happens - it seems the battery percentage the unit reports is being affected by the size of the load on the unit.

When on battery turning the load on and off causes the battery charge status to go down and up.

Here is the vid:

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

May as well return it, not right when the battery drops like that.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

Just to add, when mine was broken the battery pack would be 47 volts but the UPS thought it was 54 volts, you have no drift just knackered batteries by the looks of it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

FWIW I don't think it's the batteries. The ups was bought without and they are new batteries from a reputable supplier here in the UK. 

I'll talk to the seller about a return. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

From the UPS Front panel, did you tell the UPS that it had New batteries?

See what the UPS say the last battery change date was.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

Hey, yea new battery installed and date changed to reflect this.

I am just waiting for it to read 100% so I can do a run-time calibration via PowerChute as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

I ran a calibration test with roughly 50% load - the UPS this time dropped to around 50% (47 to be exact) like normal, but has not immidiately returned to 80+% upon removing the load - it has remained at 47% and charging.

So that's different at least - fingers crossed it means something. Not done the runtime calibration yet. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

So... after the above mentioned Calibration test and then a runtime calibration the unit is much better... so much so that I think it will probably do me for the price I paid (under £80).

Now, with a 50% load if I unplug the mains the unit doesn't immediately drop, but over a few seconds drops to 85ish% - much better than before.

If I switch the load off and then back on again the unit does initially drop to 45-50%, but then builds back up again to around 85%.

I'll grab a quick video of the above to see if it looks more 'normal'.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

Here is the video of how it is behaving now:

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore