How can "Air Cooled-ACRD" units to be switched ON automatically, when "Chilled Water-ACRC" units turn OFF?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How can "Air Cooled-ACRD" units to be switched ON automatically, when "Chilled Water-ACRC" units turn OFF?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
5
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

How can "Air Cooled-ACRD" units to be switched ON automatically, when "Chilled Water-ACRC" units turn OFF?

Hello everyone!

I got some project, with already bought units and plan how it should work. I need Your help, because don't have much of experience in this.

I have ACRC502, ACRC301S, ACRD502, ACRD101. I need "Air Cooled" units to be switched ON automatically, when "Chilled Water" units turn OFF. How can it be done? What are possible different configuration? what kind of extra units should be used, if needed?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • acrc
  • acrd
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

Hello.

For the input contact, it will need +12 or +24 volts DC. You can either use the unit's +12 or +24 volts or supply the voltage from another source. The best place to see the wiring of the input contact is on page 29 of the ACRD100 installation manual. This is the same wiring for all the InRow units for the input contact.

For the output contact, this is just a dry contact. No voltage is used.

Thank you

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

Hello 

     To accomplish this I am assuming that you are only looking to turn on the air cooled units when something happens to the chiller and the chilled water units are no longer able to maintain room temperature. If you are looking for a different configuration then this, please let us know. There is no direct communication between the air cool and chilled water units. The Air cooled (ACRD101 and ACRD502) units will need to be controlled but the remote off contacts (see page 26 of the install manual for wiring). These will need to be wired to a relay or switch to keep these units off normally. The relay/switch will need to be controlled by either the chiller or the chilled water units. I would recommend the chiller be used as the control. This is to prevent an error on one of the chilled water units from mistaking turning on the Air cooled units. The relay/switch could also be controlled by a temperature sensor (or other sensor) in the room as well. When the chiller goes down or the temperature in the room got to high, the relay/switch would flip and allow the Air cooled units to turn on to cool the room.

     The Air cooled units will show an alarm of "On standby, input contact fault exists." while the chilled water units are working. You can use the Chilled water unit's output relay to control the relay. You will need to make sure the relay can be controlled by dry contacts. The unit’s output relay is just a set of dry contacts. You will also need to configure the output relay on the unit to only alarm on critical alarms so the unit does not swap over on a noncritical alarm. This can be done through the front screen. Again I would recommend seeing if the chiller can send a signal to control the relay instead of the chilled water units or to use an external sensor. If you need any clarification on this or have any more questions please let reply or give us a call. Please check our website www.apc.com and the contact link at the bottom right to find the appropriate number for your country.

Thank you


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:06 AM

Hello!

     Yes, I was looking to turn on the air cooled units when something happens to the chiller and the chilled water units are no longer able to maintain room temperature. I read out that there is no direct communication between the air cool and chilled water units by A-Link. If Air cooled (ACRD101 and ACRD502) units can be controlled but the remote off contacts, then it suits my purpose.

     Still, I have some questions. As I read at page 32 of InRow RD Installation manual (regarding to ACRD502), Customer input +  is used for remote shutdown of the InRow RD. Voltage is applied from the internal power supply or by using an external power supply, so exactly what input should be used to start InRow?

     The same story with ACRD101, in InRow RD 10kW Air Cooled Installation at page 25, I can see Shutdown input contacts and alarm output contacts, so I have my question again, is there any kind of input, that can start up InRow and shut it down?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

Hello.

     There is no input to start the InRow unit. The process is to keep the unit in remote shutdown until the unit is needed. When you release the remote shutdown the unit will start cooling provided it sees a demand for cooling (this depends on the setpoint that the unit is configured to maintain. These are set under the group setpoints menu on the unit).  The only other thing you will need to do is to turn the unit from "standby" to "on" through the front screen before you apply the remote shutdown. This will cause the unit to maintain the setpoint that it was set to, once the remote shutdown is released. I hope this clarifies your question. Let us know if it does not.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
0
1046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

Hello.

     Regarding to theme above, can I use relays and 12/24 Vdc, to complete this connections? In manuals it's written "Customer input + (12–30 Vac/Vdc, 24 Vdc @ 11 mA)"  and "Supply 12 Vdc (current limit: 20 mA)"/"Supply 24 Vdc (current limit: 20 mA)", is it okey to give power from Supply to Customer input, wont it be over-current?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
0
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:07 AM . Last Modified: ‎2024-03-18 12:05 AM

Hello.

For the input contact, it will need +12 or +24 volts DC. You can either use the unit's +12 or +24 volts or supply the voltage from another source. The best place to see the wiring of the input contact is on page 29 of the ACRD100 installation manual. This is the same wiring for all the InRow units for the input contact.

For the output contact, this is just a dry contact. No voltage is used.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of