Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:43 AM
Hello,
I have the following UPS:
-------------------------
UPS
Model: Smart-UPS X 1500
SKU: SMX1500RMI2U
Firmware Revision: UPS 09.1 (ID20)
Manufacture Date: 08/23/2012
NMC
Model Number: AP9631
Hardware Revision: 05
Manufacture Date: 10/11/2012
APC OS (AOS)
Name: aos
Version: v6.0.6
APC Boot Monitor
Name: bootmon
Version: v1.0.2
-------------------------
I am trying to change the default event actions, particularly I don't want to be emailed about informational events. In the Network Management Card web interface, I tried going to Configuration->Notification->Event Notifications->By Group, unticking "All Informational Events" and completing the wizard, however the UPS keeps emailing informational events. As you can see the checkbox remains checked after completing the wizard:
I have also tried going to Configuration->Notification->Event Notifications->By Event->Diagnostics and disabling email action for all events in the Informational category however I am still getting "UPS: passed via internal operation a self-test." emails.
If someone can please explain to me what I'm missing that would be greatly appreciated. Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:43 AM
gotzapped,
Without having time to post a screen shot i recommend this:
Login to your device, go to the notification (you call it diagnostics) screen and click on the "UPS Self test Failed" event. At the top, in the URL, you will see the "event code" at the end. replace the existing event code with the code in the email you don't want to receive (in this case code 0x0105). You should get a familiar screen with the event options however you SHOULD see "Informational - UPS: passed via internal operation a self-test." as the event. It is a little hidden screen.
I too did not want these alerts. Not sure why they are hidden.
Regards,
J
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:43 AM
The way you should be doing it is selecting the checkbox for all of the events you don't want and going through the wizard and selecting disable notifications.
Passed a self test is considered a "clearing" event. The event you're showing in the screenshot is "UPS: Self test failed" and I guess I'd call that the actual event that "passed a self test" clears. Please refer to this article and review the disclaimer and as long as you accept it, you can review the steps in the article to disable the passed self event -> Configuring clearing events with APC Network Management Cards | FAQs | Schneider Electric ITB
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:43 AM
Angela,
Thank you for the prompt advice. Sorry for the delayed response, I have been away.
I have just followed your advice. Thanks for point out where I was wrong as I couldn't have figured this out myself - documentation doesn't make the correct procedure clear enough.
I will report back to advise whether this has resolved our issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:43 AM
Hi Angela,
We are still getting these alerts:
-----------------------------
Name : UPS01
Location : Server Room
Contact : Contact Name
Serial Number :
Device Serial Number :
Date : 02/11/2014
Time : 19:15:08
Code : 0x0105
Informational - UPS: passed via internal operation a self-test.
-----------------------------
I wonder what I'm missing? Thanks
**EDIT**:
Just re-read your previous post and followed the steps to configure the Clear events. I will post back to update.
Message edited due to not reading entire previous post
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:09 AM . Last Modified: 2024-03-05 01:43 AM
gotzapped,
Without having time to post a screen shot i recommend this:
Login to your device, go to the notification (you call it diagnostics) screen and click on the "UPS Self test Failed" event. At the top, in the URL, you will see the "event code" at the end. replace the existing event code with the code in the email you don't want to receive (in this case code 0x0105). You should get a familiar screen with the event options however you SHOULD see "Informational - UPS: passed via internal operation a self-test." as the event. It is a little hidden screen.
I too did not want these alerts. Not sure why they are hidden.
Regards,
J
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.