Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
USB communication problem from 2009 — any update?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3002:36 AM. Last Modified: 2024-03-1011:15 PM
USB communication problem from 2009 — any update?
Looking for updates on something that was discussed here in 2008/2009 . . . .
There was a thread in this forum ("Communication Lost in a Smart UPS 1500 with USB") about a problem several people were having, in which an APC UPS would stop talking to its server. The problem could be cleared up by unplugging the USB data cable and plugging it back in, but this was only a temporary solution until the next time the problem would show up (and obviously not feasible at all if the server was far away).
An APC person said it appeared the problem had to do with a USB 2.0 protocol issue, and that a workaround could involve either reconfiguring the server's USB ports down to the old, slow 1.1 protocol, or using an RS232 serial cable instead of a USB cable. Not surprisingly, several frustrated users proposed the even more permanent solution of abandoning APC and switching to some other UPS manufacturer. (!!)
Anyway, I wanted to find out whether this problem has been fixed in newer APC UPS'es, or if it still affects APC's new products today. I'm having a problem that sounds suspiciously like this, with a Back-UPS XS 1500 (manufactured in 2006, battery replaced last September), connected to my desktop running Ubuntu Linux (Maverick), and using the "apcupsd" monitoring software. Since APC's products appear to be the best supported UPS'es for Linux, I'm hesitant to switch to a different manufacturer for my future purchases if I can avoid it.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3002:36 AM. Last Modified: 2024-03-1011:15 PM
i have not heard of any issues with the next generation SMT/SMX models of Smart UPS and USB communication loss but i cannot say i have tested it extensively.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3002:36 AM. Last Modified: 2024-03-1011:15 PM
i have not heard of any issues with the next generation SMT/SMX models of Smart UPS and USB communication loss but i cannot say i have tested it extensively.