Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Incorrect reported runtime after calibration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Incorrect reported runtime after calibration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
rajil.s_apc
Crewman rajil.s_apc
Crewman

Posted: ‎2021-06-30 02:36 AM . Last Modified: ‎2024-03-10 11:15 PM

0 Likes
0
959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:36 AM . Last Modified: ‎2024-03-10 11:15 PM

Incorrect reported runtime after calibration

Sorry i had posted in the wrong forum, so reproducing here.


Hi,

I bought a new APC SUA1000UXI UPS about a month ago. The UPS is running over two 12V Exide 7AH batteries. Over the past one month the reported runtime (using apcupsd/suse linux) decreased from about 120 minutes to about 7 minutes. I reported to APC customer care and an engineer was sent out to have a look. It seemed there was a calibration problem and the service centre guy corrected the battery constant to '7F'. Now the UPS is again reporting a run time of 112 minutes at 11 percent load.

To verify that the runtime was accurate i switched off the main and let the UPS run until it drained itself. The batteries died in about 11 minutes. I have specified a minimum remaining time of 2 minutes and minimum battery charge of 5%. So the actual backup time could be about 10 minutes. Is there a problem with the UPS? The batteries are new. If somebody is tracking the APC support emails, the incident number for this is Incident: 110530-000011.

The battery characteristics recorded just before and after i killed the mains are below. The UPS was showing remaining time of 91 minutes before i killed the power at 21:02. The next recording at 21:10 showed a remaining time of 20 minutes and the UPS shut itself off at 21:12. After the UPS charged the batteries to 100% capacity, the reported backup time has again risen to 118 minutes.

Date Time Remain Batt % Remain Battery Voltage Temp Line Frequency Line Voltage Load %
5/30/2011 20:55 91 100.0 27.40 33 50 218.80 13.60
5/30/2011 21:00 91 100.0 27.40 33 50 216.02 13.60
5/30/2011 21:05 47 52.3 24.22 32 50 1.44 13.60
5/30/2011 21:10 20 23.1 22.90 32 50 0.00 14.30
5/30/2011 21:30 62 65.0 27.30 34 50 252.00 13.60
5/30/2011 21:35 68 68.0 27.30 34 50 254.78 12.31
5/30/2011 21:40 71 71.0 27.40 33 50 253.41 12.30
5/30/2011 21:45 71 75.0 27.40 33 50 249.11 13.00
5/30/2011 21:50 74 78.0 27.40 33 50 250.49 12.31
5/30/2011 21:55 82 82.0 27.40 33 50 249.11 13.00
5/30/2011 22:00 86 86.0 27.40 33 50 253.37 12.30
5/30/2011 22:05 89 89.0 27.40 33 50 250.53 12.30
5/30/2011 22:10 92 92.0 27.30 33 50 249.11 13.00
5/30/2011 22:15 96 96.0 27.40 33 50 247.61 12.30
5/30/2011 22:20 100 100.0 27.40 33 50 250.48 12.30
5/30/2011 22:25 100 100.0 27.40 33 50 249.11 12.30
5/30/2011 22:30 100 100.0 27.40 33 50 244.83 13.00
5/30/2011 22:35 95 100.0 27.40 33 50 246.19 12.30
5/30/2011 22:40 100 100.0 27.40 33 50 241.91 12.30
5/30/2011 22:45 118 100.0 27.40 33 50 236.14 9.12
5/30/2011 22:50 118 100.0 27.40 33 50 240.37 9.10

Thanks
Rajil

Message was edited by: rajil.s

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • calibration
  • smart-ups
  • sua1000uxi
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore