URGENT - Repair assistance needed - MATRIX 5000 failures

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • URGENT - Repair assistance needed - MATRIX 5000 failures
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:52 PM

0 Likes
7
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:52 PM

URGENT - Repair assistance needed - MATRIX 5000 failures

I have posted before on this issue, but it has become urgent.

I need to speak with ANYONE that can assist with diagnosing the failures we are having on both APC MX5000xx units.

One unit has a charger failure, the other flops between MAIN and BYPASS RLY FAULT.

 

I would be happy to pay someone for their time to assist us.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:50 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:50 PM

It seems that matrix has 3843 instead of 2843. It is the one marked CS3843 sightly offset left of the small signal transformer. The reason I'd check for battery charge voltage is so that we don't try to fix something that is not broken & get more specific about the issue. The voltage measurement at the battery pack could help to determine the nature of charger failure, eg. too high/too low/nonexistent charge voltage or false alarm. 

I don't have any schematics for the unit, so I cannot tell which relay is the one. As per my previous post, I'd simply replace all the electrolytic caps on the board (with same uF rating, slightly higher voltage rating of the original capacitor), maybe also check the semiconductors in the vicinity of the relays, then try and see if the problem is gone. 

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:52 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:52 PM

Hi,

Try CoastTec.com They repair single phase APC UPS. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:52 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:52 PM

Yea, I already called them and I'm hoping they can help.
So far they say they don't anymore, but the sales guy said he would try to connect me with someone.

 

HOWEVER, if there is ANYONE out there that feels confident they can assist me with determining where on the board I can look for diagnosing this issue, please chime in.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:52 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:52 PM

Hello, 

From what I read in your previous topic, you already disassembled and reassembled them, so I assume you have some electronics skills to do component level repairs. The following things that I am going to write come from my personal experience with APC units in general, and info that was read on the net. Although I have a disfunctional matrix unit, I did not yet have time to disassemble and repair it. Relay issue: I'd go and check electrolytic capacitors on the control board where the relays are located. They are bound to fail after decades of operation, especially smaller capacitance ones. If DC power supply becomes unreliable, it might cause this issue even if the relays themselves are OK. 

Battery charger failure: what is the exact symptom? Error message on LCD, and no charging voltage measured at battery pack? In smaller apc units, battery charging is done using UC2843 IC, I'd start debugging around it. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:51 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:51 PM

Thanks for the advice.

Regarding the battery charger, yes - the LCD said that the charger had faulted.

I can reassemble it and check the voltage to the batteries, but unless you feel it's likely a false alert, then I'm willing to trust it.
I'll get started on the testing process and get back to you, but would you be available to discuss this as I proceed through the boards?

Also, for the community, I'll post the progress and findings here as they happen.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:51 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:51 PM

I'm going to share some images in this thread for everyone to get on the same page as we progress.

I cannot locate the IC you refer to (UC2843) though.

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:51 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:51 PM

As I try to fix the bypass/main relay fault, where is this relay located?

Is it the large SCR? (Remove in my previous images for testing, which I have 3 of these components and they all test identical, so I assume they are good.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:50 PM

0 Likes
0
1453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:39 AM . Last Modified: ‎2024-03-07 10:50 PM

It seems that matrix has 3843 instead of 2843. It is the one marked CS3843 sightly offset left of the small signal transformer. The reason I'd check for battery charge voltage is so that we don't try to fix something that is not broken & get more specific about the issue. The voltage measurement at the battery pack could help to determine the nature of charger failure, eg. too high/too low/nonexistent charge voltage or false alarm. 

I don't have any schematics for the unit, so I cannot tell which relay is the one. As per my previous post, I'd simply replace all the electrolytic caps on the board (with same uF rating, slightly higher voltage rating of the original capacitor), maybe also check the semiconductors in the vicinity of the relays, then try and see if the problem is gone. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of