UPS1000 alarms every fortnight

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS1000 alarms every fortnight
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

0 Likes
12
2481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

UPS1000 alarms every fortnight

Our SmartUPS 1000 fails every fortnight. The alarm sounds and the output fails. It switches over to battery, which drops immediately and the attached equipment powers off. Photos taken at the time show The overload and replace battery indicators lit - see attached.

The ups power needs to be unplugged. When plugged back in the equipment powers up and the battery recharges in a few hours.

I understand my predecessor replaced the battery within the last year.

A manual test does not cause this issue.

Can anyone advise me the way to resolve this please?

Attachments
ups.zip
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-18 12:43 AM

0 Likes
0
2479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-18 12:43 AM

On 1/24/2018 12:56 PM, Bill said:

Switch the driver HID UPS Battery to APC UPS

Hi,
I tried the steps to update the drivers.

Driver update does not find the APC driver on my laptop (windows 10 pro).

It insists the HID one is the only one.

I can't find anywhere to download the APC driver from.

The battery fail light is illuminated all the time, so I'm going to get a new battery.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

0 Likes
0
2479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

Hi Malcolm - 

that LED indicates an Overload. What do you have connected to the UPS? How many LED's are normally lit on the left hand side column?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

0 Likes
0
2479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

Hi Liam,

From what I can see the load is a “small” HP server (+ monitor that is usually off), BT broadband modem, router and a couple of network switches.

 I can’t remember the lights. I will check when I am next on site which will be Monday and post then.

M

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

0 Likes
0
2479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

Hi,

 I just spoke to the office. In normal operation none of the lights on the left are lit.

M

Reply

Link copied. Please paste this link to share this article on your social media post.

Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

0 Likes
0
2479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

When the batteries were dead in one of my older APC units, it would drop the load every fortnight when it went to do the self test.  Quite annoying because the UPS caused more outages than it prevented.  I was able to work around the problem by changing the settings to disable the self test, but of course the batteries were still dead so in a power outage everything switched off immediately.  But at least it stopped the extra outages until I was able to replace the batteries!

As the batteries were dying though, it got to the point where they could sustain a small load like a light bulb, but they'd switch off when powering anything bigger, owing to the fact that the apparent capacity of lead acid batteries reduces as you draw more current.  So my guess is that your batteries are about to die.

If you are sure they were only replaced a year ago (check the battery replacement date in the UPS config) then they could have just been a bad/cheap batch, or new old stock.  If you bought from a reputable supplier maybe you will have warranty options you can explore, but warranties around one year or longer aren't common for batteries, going to show just how long they are expected to last for!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

0 Likes
0
2479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

In the office during normal (mains powered) operation none of the left hand lights are lit. 

The user guide seemed to suggest they only light when the ups is providing power, so I briefly turned off the mains power (I didn’t want the server to go down). None of the left hand lights lit then either.

Reply

Link copied. Please paste this link to share this article on your social media post.

Malvineous_apc
Lieutenant Malvineous_apc
Lieutenant

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

0 Likes
0
2479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:44 AM

What happens if you run a calibration (this is different to a self test.)  It will run off batteries until they are nearly flat then switch back to mains to more accurately calculate the runtime, so it won't power off your load (unless there's a fault of course.)

It sounds like you have bad batteries so I would expect the calibration to fail or complete in only a minute or two, indicating minimal battery capacity available.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:43 AM

0 Likes
0
2479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:43 AM

Thanks for the suggestion, Adam.

At the moment there is no data connection to the ups and it doesn’t have lcd screen.

I can find no trace of any original cables or software. I guess I’ll see if I can find a usb cable , download the powerchute software and have a go. That will be next week.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:43 AM

0 Likes
0
2479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:43 AM

Well, I tried USB cable to my Win10 laptop. The UPS driver seemed to install OK.

Tried Powerchute but it refuses to find the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:43 AM

0 Likes
0
2478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:43 AM

Hi,

What is the exact model and serial numbers of the Smart-UPS? you will find them on the bar code sticker on the back of the unit.

6cT7T06MeP%2BLLovs5KBM%2FA%3D%3D.png6cT7T06MeP%2BLLovs5KBM%2FA%3D%3D.png

As for PowerChute, when you attached the USB cable did the laptop report it found new hardware? If so, when the cable is connected what drivers are displaced. You will find the drivers in the control panel - device manager - battery and under human interface devices. 

See Schneider Electric FAQ FA310907 for assistance with the drivers. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:43 AM

0 Likes
0
2478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:15 AM . Last Modified: ‎2024-03-18 12:43 AM

Hi Bill,

Model: SUA1000I

Serial: AS0709330154

The Device Manager has installed drivers showing in

Batteries as 'HID UPS Battery'

and

Human Interface Devices as 'American Power Conversion USB UPS'

Driver details are shown the attached pics.

I have the .sys files but not the .inf

Regards

Malcolm

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-18 12:43 AM

0 Likes
0
2478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-18 12:43 AM

Hi,

Switch the driver HID UPS Battery to APC UPS. See Schneider Electric FAQ FA164514 for assistance with changing the driver. After changing the driver run the PowerChute installer again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-18 12:43 AM

0 Likes
0
2480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:16 AM . Last Modified: ‎2024-03-18 12:43 AM

On 1/24/2018 12:56 PM, Bill said:

Switch the driver HID UPS Battery to APC UPS

Hi,
I tried the steps to update the drivers.

Driver update does not find the APC driver on my laptop (windows 10 pro).

It insists the HID one is the only one.

I can't find anywhere to download the APC driver from.

The battery fail light is illuminated all the time, so I'm going to get a new battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore