Hello everyone,
We have a Smart-Ups X 1000 and every 4-5 days the UPS turns itself off. It must therefore be turned on manually via the on/off button.
In the log we can see the following messages :
2022-06-01 - 22:29:42 - On Line (Green Mode) - Exited
2022-06-01 - 22:29:42 - PowerChute Agent outlet turning off (by external entity)
2022-06-01 - 22:29:42 - Monitoring Stopped
The UPS is connected via USB to an HP Proliant server with Windows server 2022.
There is never anyone in the offices when this is happening.
Has anyone had this problem before?
Thank you in advance, have a nice day.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-06 09:32 AM
I recommend you turn off green mode. From the LCD panel of the UPS go to Configuration - Green Mode - Disable. The check the Event Log to see if the UPS recorded outlet group off at the time PowerChute recorded it.