Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
Hi,
Can you please help me recommend a UPS on the below specification:
Equipment to support:
1x CISCO2811-HSEC/K9 2811 Bundle w/AIM-VPN/SSL-2,Adv IP Serv,10 SSL lic,128F/512D
1x WS-C3560V2-24PS-S Catalyst 3560V2 24 10/100 PoE + 2 SFP + IPB (Standard) Image
Is it right to recommend a APC Smart-UPS 2200VA RM 2U LCD 120V ?
Please for your reply asap..thanks
Message was edited by: eivan3187
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
Basically when power returns to supply power to the load (if the batteries completely dies and the ups will begin to charge the batteries in this case the SMT2200RM2U will take 3 hours to charge the battery to 90% from a complete depletion (the batteries died and the ups turned its self off)
Also I Got The Run Time By Using The Ups Selector Here:
http://www.apc.com/tools/ups_selector/index.cfm
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
How Many Watts Total And How Much Run time Is Needed
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
The router approximately for 320W and switch for 240 watts..Each of them has a rack mount height of 1U
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
The Smart Ups 2200 Would Give You Approx 49 Minutes Of Run Time
Otherwise This Would Also Work With 52 Minutes Of Run Time
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SUA2200XL
Message was edited by: Wwallender
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
Hi Wwallender,
Thanks for the quick response. Should I also recommend a UPS with this part number SMT2200RM2U since it is 2200VA. Also, can you teach me how to determine the run time of a UPs. How did you know if it is 49 minutes or 52 minutes of Run Time?
Does the recharge time means that if the UPS is in use and after a certain time, the electricity came back after one hour, it will automatically recharge?
Please explain further what is a recharge time for a UPS.
Thanks...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
Basically when power returns to supply power to the load (if the batteries completely dies and the ups will begin to charge the batteries in this case the SMT2200RM2U will take 3 hours to charge the battery to 90% from a complete depletion (the batteries died and the ups turned its self off)
Also I Got The Run Time By Using The Ups Selector Here:
http://www.apc.com/tools/ups_selector/index.cfm
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.