Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:18 AM . Last Modified: 2024-03-13 02:58 AM
This is a new unit. When bringing the unit up and placing online everything appears normal. After some amount of time (>6 hours), the appears to go into auto shutdown. The front of the display shows the following six LED's flashing simultaneously:
AVR Trim--Amber
On Line--Green
AVR Boost--Amber
Overload--Red
On Battery--Amber
Repalce Battery--Red
There is no output from the receptacles in the back of the unit. The batteries show a full charge as indicated by a voltmeter. This unit has an external battery pack (APC SUA 48XLBP) and does this with the battery pack either connected or not connected (internal batteries only).
I don't have power chute to look up any codes.
What have I got here?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
the problem started after many power outages.
So the batteries are changed
battery date is nov 2013
but the problem persists
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:58 AM
Hello I have a smart ups apc ups 3000XL 4 batteries to replace, but to cut the electrical supply the full charge indicator LEDs very quickly down to minimum, and occasionally blink led the two center columns. -
Would appreciate can help
regards
Federico
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:58 AM
Thanks for responding.
I Change 4 batteries with new
But when I disconnect the ups. LEDs full load down to minimum quickly.
Live in Argentina in Misiones Eldorado
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
You have already posted this question multiple times..no need to post it numerous times please. If you need immediate support, you can always reach out to your local technical support contacts via http://www.apc.com/support/contact/index.cfm
As far as what you asked, I can't quite understand it unfortunately.
What does "but to cut the electrical supply the full charge indicator LEDs very quickly down to minimum" mean? Could you please reword it? I am thinking maybe it means that with your 4 batteries require replacement, the battery charge drops quickly? If the batteries are faulty and need replacing, this could happen. If the batteries are new, you'd want to make sure they've been charging for several hours before trying to do anything.
If the center 6 LEDs are flashing, this typically indicates an Automatic Voltage Regulation (AVR) relay weld and likely comes when AVR operation happens. If the relay is welded, the unit may require repair, if available in your region, or replacement.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
How long have those batteries been charging without any touching? Make sure at least 24 hours to really verify if a problem or not. And how much load is attached to the UPS? (you can check the far left graph and see how many LEDs are lit)
Lastly, are these genuine APC replacement batteries or third party? Is there any date code on the batteries to verify they are not too old or have been sitting?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Fedeico Gonzalo Artús respondido (en respuesta a Angela N.) 10-ene-2014 12:06
Thanks for responding.
I Change 4 batteries with new
But when I disconnect the ups. LEDs full load down to minimum quickly.
Live in Argentina in Misiones Eldorado
the problem started after many power outages.
So the batteries are changed
battery date is nov 2013
but the problem persists
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Hurray , Finally by just changing the 5 relays , the unit is back to life , now i am testing the unit and we will see what happens and how it runs .
And by the way thank you all .
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
hello everyone ,
i have the same problem with my ups but i have no warranty .
Angela N. what do you mean by avr relay weld , do you mean it is defective or the
soldering is defective , i can change the relay if you have info on what relay to change
in the circuit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
I mean the relay is welded and these are not intended to be user serviceable so proceed at your own risk. If you have this condition, the recommendation is to replace the UPS one way or the other.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
ok thanks i will replace the faulty welded relays and check it works , thanks for your reply.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
In all likelihood it might not be "just the relay(s)" that are at fault in these situations. Relays are engineered not to weld themselves under normal current / switching loads. However if the relay(s) were overloaded by a short circuit or overload downstream of the relay - eg a shorted winding in one of the transformers or some other output stage of the UPS faulty then they may arc/fuse. If you are bent on self-repair i'd recommend thoroughly going over the rest of the unit, lest you spend time and money on relays only to have them fuse the moment you stick them in.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
@battman , thanks for your comment ,
- I have dismantled the unit.
- I have checked the relay contacts for normally closed and normally open contacts.
- The relay on a deenergized state are looking fine , however i cannot be sure if the normally close contacts are welded or not , only if i apply 24v to the relay , i can confirm that .
- Now the plan of action is to check the relay with a hot test to confirm all the contacts are working ,
Well i hope that it is only the relay problem as the unit is quite old , it says 2005 on the PCB.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Well to my utter disappointment , i have desoldered the relay and tested all the five relays , and they are working fine , but still i am changing them , i am also looking for some other faults in the circuit meanwhile.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
the center 6 LEDs flashing indicate an AVR relay weld unfortunately. AVR relates to the automatic voltage regulation so if you are seeing this, then i'd recommend you contact APC for a warranty replacement and tell them this is what you see on the front panel. since its brand new, it will be covered under warranty when you provide the serial number.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Thanks for the reply. I appreciate your help!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:19 AM . Last Modified: 2024-03-13 02:57 AM
the problem started after many power outages.
So the batteries are changed
battery date is nov 2013
but the problem persists
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of