Smart UPS 3000XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 3000XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:18 AM . Last Modified: ‎2024-03-13 02:58 AM

0 Likes
15
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:18 AM . Last Modified: ‎2024-03-13 02:58 AM

Smart UPS 3000XL

This is a new unit. When bringing the unit up and placing online everything appears normal. After some amount of time (>6 hours), the appears to go into auto shutdown. The front of the display shows the following six LED's flashing simultaneously:
AVR Trim--Amber
On Line--Green
AVR Boost--Amber
Overload--Red
On Battery--Amber
Repalce Battery--Red
There is no output from the receptacles in the back of the unit. The batteries show a full charge as indicated by a voltmeter. This unit has an external battery pack (APC SUA 48XLBP) and does this with the battery pack either connected or not connected (internal batteries only).
I don't have power chute to look up any codes.
What have I got here?

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

the problem started after many power outages.

So the batteries are changed

battery date is nov 2013

but the problem persists

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:58 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:58 AM

Hello I have a smart ups apc ups 3000XL 4 batteries to replace, but to cut the electrical supply the full charge indicator LEDs very quickly down to minimum, and occasionally blink led the two center columns. -

Would appreciate can help

regards

Federico

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:58 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:58 AM

Thanks for responding.

I Change 4 batteries with new

But when I disconnect the ups. LEDs full load down to minimum quickly.

Live in Argentina in Misiones Eldorado

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

Hi federicoartus

You have already posted this question multiple times..no need to post it numerous times please. If you need immediate support, you can always reach out to your local technical support contacts via http://www.apc.com/support/contact/index.cfm

As far as what you asked, I can't quite understand it unfortunately.

What does "but to cut the electrical supply the full charge indicator LEDs very quickly down to minimum" mean? Could you please reword it? I am thinking maybe it means that with your 4 batteries require replacement, the battery charge drops quickly? If the batteries are faulty and need replacing, this could happen. If the batteries are new, you'd want to make sure they've been charging for several hours before trying to do anything.

If the center 6 LEDs are flashing, this typically indicates an Automatic Voltage Regulation (AVR) relay weld and likely comes when AVR operation happens. If the relay is welded, the unit may require repair, if available in your region, or replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

How long have those batteries been charging without any touching? Make sure at least 24 hours to really verify if a problem or not. And how much load is attached to the UPS? (you can check the far left graph and see how many LEDs are lit)

Lastly, are these genuine APC replacement batteries or third party? Is there any date code on the batteries to verify they are not too old or have been sitting?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

Fedeico Gonzalo Artús respondido (en respuesta a Angela N.) 10-ene-2014 12:06

Thanks for responding.

I Change 4 batteries with new

But when I disconnect the ups. LEDs full load down to minimum quickly.

Live in Argentina in Misiones Eldorado

the problem started after many power outages.

So the batteries are changed

battery date is nov 2013

but the problem persists

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

Hurray , Finally by just changing the 5 relays , the unit is back to life , now i am testing the unit and we will see what happens and how it runs .

And by the way thank you all .

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

hello everyone ,

i have the same problem with my ups  but i have no warranty .

Angela N. what do you mean by avr relay weld , do you mean it is defective or the

soldering is defective , i can change the relay if you have info on what relay to change

in the circuit.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

I mean the relay is welded and these are not intended to be user serviceable so proceed at your own risk. If you have this condition, the recommendation is to replace the UPS one way or the other.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

ok thanks i will replace the faulty welded relays and check it works  , thanks for your reply.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

In all likelihood it might not be "just the relay(s)" that are at fault in these situations. Relays are engineered not to weld themselves under normal current / switching loads. However if the relay(s) were overloaded by a short circuit or overload downstream of the relay  - eg a shorted winding in one of the transformers or some other output  stage of the UPS faulty then they may arc/fuse. If you are bent on self-repair i'd recommend thoroughly going over the rest of the unit, lest you spend time and money on relays only to have them fuse the moment you stick them in.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

@battman , thanks for your comment ,

- I have dismantled the unit.

- I have checked the relay contacts for normally closed and normally open contacts.

- The relay on a deenergized  state are looking fine , however i cannot be sure if the normally close contacts are welded or not , only if i apply 24v to the relay , i can confirm that .

- Now the plan of action is to check the relay with a hot test to confirm all the contacts are working ,

Well i hope that it is only the relay problem as the unit is quite old , it says 2005 on the PCB.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

Well to my utter disappointment , i have desoldered the relay and tested all the five relays , and they are working fine , but still i am changing them , i am also looking for some other faults in the circuit meanwhile.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

the center 6 LEDs flashing indicate an AVR relay weld unfortunately. AVR relates to the automatic voltage regulation so if you are seeing this, then i'd recommend you contact APC for a warranty replacement and tell them this is what you see on the front panel. since its brand new, it will be covered under warranty when you provide the serial number.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

Thanks for the reply. I appreciate your help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

0 Likes
0
1481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:19 AM . Last Modified: ‎2024-03-13 02:57 AM

the problem started after many power outages.

So the batteries are changed

battery date is nov 2013

but the problem persists

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of