UPS reset power when trying to run Self Test

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS reset power when trying to run Self Test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
cake756
Crewman cake756
Crewman

Posted: ‎2024-03-17 07:22 PM

0 Likes
2
1117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-17 07:22 PM

UPS reset power when trying to run Self Test

Hi there,

 

We have a APC Easy UPS SMV 3000VA 230V. Last week, we had a power cut. While a number of devices connected to the UPS were set up to shutdown gracefully via UPSMON, those devices simply lost power and all went offline at the same time. So today, I wanted to do a Self Test (by connecting to UPSCAPO via a USB cable.) The UPS simply had a power reset instead of running the test. So, all connected devices were either lost power abruptly or rebooted. 

 

The status says the battery is fully changer when I checked on UPSCAPO. 

 

Just wondering if anyone would know if that indicates a battery problem or perhaps something else please?

 

Thanks,

 

Edmond.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2024-03-19 09:45 AM

0 Likes
1
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-19 09:45 AM

The batteries are rated to provide 3-5 years of service life based on usage and environmental factors such as heat. If the batteries are more than five years old it’s time to replace them.

 

Based on your description of what happens upon a self test the cartridge are  bad and need to be replaced. You can validate this easily by removing AC Power.

 

If the unit turns off immediately this indicates the batteries are expired. If you take the battery cartridge apart and measure each cell you’ll probably find one or more cells are below 12.80 VDC. 

Keep in mind if you measure the voltage right when you remove the cartridge it will show above 12.80 VDC. Hence why you will need to let the battery sit and rest for 72 hours. If you come back and the voltage is below 12.50 - 12.70 VDC or below the cells are bad.

 

As a good cell won’t lose any voltage in just 72 hours. ☝️A more accurate test is to perform a load test based on the data sheet. This is followed by measuring the internal resistance of each cell and comparing it to the battery makers data sheet.

 

If the internal resistance is stated as 20 mOhms. And you measure double, triple the value or beyond the cell is toast from sulfication. 

Keep in mind you could also measure no resistance which indicates a dead short! A dead short would quickly drain any connected cells in the pack which reduces the overall service life of the cartridge.

 

Report back what you measure and observe. You’ll want to order a RBC which can be found on the LCD as to the model number if the unit is under warranty. If the unit is NOT under APC warranty you can simply rebuild the pack with high output CSB battery cells that come with the unit anyways! 👍

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Teken
Kirk Teken
Kirk

Posted: ‎2024-03-19 09:45 AM

0 Likes
1
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-19 09:45 AM

The batteries are rated to provide 3-5 years of service life based on usage and environmental factors such as heat. If the batteries are more than five years old it’s time to replace them.

 

Based on your description of what happens upon a self test the cartridge are  bad and need to be replaced. You can validate this easily by removing AC Power.

 

If the unit turns off immediately this indicates the batteries are expired. If you take the battery cartridge apart and measure each cell you’ll probably find one or more cells are below 12.80 VDC. 

Keep in mind if you measure the voltage right when you remove the cartridge it will show above 12.80 VDC. Hence why you will need to let the battery sit and rest for 72 hours. If you come back and the voltage is below 12.50 - 12.70 VDC or below the cells are bad.

 

As a good cell won’t lose any voltage in just 72 hours. ☝️A more accurate test is to perform a load test based on the data sheet. This is followed by measuring the internal resistance of each cell and comparing it to the battery makers data sheet.

 

If the internal resistance is stated as 20 mOhms. And you measure double, triple the value or beyond the cell is toast from sulfication. 

Keep in mind you could also measure no resistance which indicates a dead short! A dead short would quickly drain any connected cells in the pack which reduces the overall service life of the cartridge.

 

Report back what you measure and observe. You’ll want to order a RBC which can be found on the LCD as to the model number if the unit is under warranty. If the unit is NOT under APC warranty you can simply rebuild the pack with high output CSB battery cells that come with the unit anyways! 👍

 

Reply

Link copied. Please paste this link to share this article on your social media post.

cake756
Crewman cake756
Crewman

Posted: ‎2024-03-20 06:23 PM

In response to Teken
0 Likes
0
1069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-20 06:23 PM

Thank you so much for the comprehensive instruction. I have planned an outage tomorrow so will be able to do some of the tests you have mentioned. Probably can't disconnect the battery for a prolonged period of time, but hopefully I can determine the root problem.

 

Cheers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore