Smart UPS Modular Ultra 20kW no longer detects battery modules.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS Modular Ultra 20kW no longer detects battery modules.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
GregF34
GregF34
Cadet

Posted: ‎2024-03-18 10:01 AM

0 Likes
2
565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-18 10:01 AM

Smart UPS Modular Ultra 20kW no longer detects battery modules.

Smart-UPS Modular Ultra 20kW no longer detects battery modules. The UPS was working fine. No changes were made to the UPS configuration. Suddenly the UPS is showing an error message "Invalid Configuration - not operational battery modules installed". 

 

UPS Model : SRYLF20KRMT

Batty frame X2: SRYLFXBPRM4

 

The UPS has 4 power modules and 8 battery modules in total. Two battery modules are inserted into UPS frame and the rest of 6 battery modules are inserted into the XBP battery frame one and two. 

 

Rebooting the UPS did not fix the problem. 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Janeway Teken
Janeway

Posted: ‎2024-03-19 09:23 AM . Last Modified: ‎2024-03-20 07:13 AM

0 Likes
0
558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-19 09:23 AM . Last Modified: ‎2024-03-20 07:13 AM

From personal experience it can be a corrupted IC in the battery pack or change in settings. I’d start by confirming all settings are correct and reviewing the error logs prior, during, and after the fault.

 

Specifically what the line quality was at that time. This would be a good time to validate all connections are sound and no corrosion is present. 

Remove one of the packs and measure the voltage. If any pack is out of specification replace and see what the results are. 

Swapping packs within the system is something you could test to see if the behaviour changes. 

Grounding: Insure all grounding for the system is present, tested, validated! ☝️

 

Bypass: If there is a bypass available enable this feature and observe what happens when it’s toggled on / off.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Teken
Janeway Teken
Janeway

Posted: ‎2024-03-19 09:23 AM . Last Modified: ‎2024-03-20 07:13 AM

0 Likes
0
559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-19 09:23 AM . Last Modified: ‎2024-03-20 07:13 AM

From personal experience it can be a corrupted IC in the battery pack or change in settings. I’d start by confirming all settings are correct and reviewing the error logs prior, during, and after the fault.

 

Specifically what the line quality was at that time. This would be a good time to validate all connections are sound and no corrosion is present. 

Remove one of the packs and measure the voltage. If any pack is out of specification replace and see what the results are. 

Swapping packs within the system is something you could test to see if the behaviour changes. 

Grounding: Insure all grounding for the system is present, tested, validated! ☝️

 

Bypass: If there is a bypass available enable this feature and observe what happens when it’s toggled on / off.

Reply

Link copied. Please paste this link to share this article on your social media post.

GregF34
GregF34
Cadet

Posted: ‎2024-03-20 07:06 AM

0 Likes
0
524
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-20 07:06 AM

I fixed the problem by shutting down the UPS and inserting the battery modules one by one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of