UPS not turning on when power comes back

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS not turning on when power comes back
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

0 Likes
8
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

UPS not turning on when power comes back

Hi,

I have a UPS,  surt2000xli which is only a month old and the situation is as follows.

The UPS is running on a floating crane which is turned off in the weekend.

After 2 or 3 days the crane powers back on but the UPS does'nt turn itself back on.

My question is, is it even possible for the UPS to detect returning power after a few days ?

Or might it have to do something with the settings ?

These are the current settings :

Time Required for Shutdown Sequence : 5 minutes

Low battery signal  2 minutes

Command file enabled : no

OS Shutdown duration : 0:20 Minutes:Seconds

OS shutdown type : Shutdown

Enable OS reboot : yes

UPS turn on battery capacity: 0%

UPS turn on Delay : 0 Minutes

Enable SMTP : No

Enable Logging : Yes

If theres any other info needed I will try to provide, since I have to physically connect to the UPS to read the logs etc.

Thanks in advance

Greetings,

Kevin


Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

0 Likes
0
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

Hello - I did some checking.

I am told for a scenario like this with really good, new batteries, it should make it 72 hours..less than ideal situations it may be less..regardless, it should wake up when AC power is applied to it in a normal situation.

I know you said its a month old but can you give me the first several digits of the serial number on it if possible to verify manufacture date? Something like JS0910XXXXXXX - thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

0 Likes
0
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

How is the UPS being turned off before the weekend? Is someone pressing the power button to turn it off because if so, it needs to be manually turned back on.

If the UPS is turning off due to a low battery condition or by software after some type of graceful shutdown, then it might be possible depending on how long that UPS can sleep for while waiting for AC power to come back.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

0 Likes
0
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

Its not manually turned off so it shuts down due to low battery condition. I've just googled for the max. sleep time but I can't seem to find it.

The previous UPS, which was the same type and died, is said to have been woken up after the weekend when the power on the crane was restored.

Do you happen to know how long the sleep time would be ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

0 Likes
0
2859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

Then I have my answer.

Thanks for the help Angela

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

0 Likes
0
2859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

Hello - I did some checking.

I am told for a scenario like this with really good, new batteries, it should make it 72 hours..less than ideal situations it may be less..regardless, it should wake up when AC power is applied to it in a normal situation.

I know you said its a month old but can you give me the first several digits of the serial number on it if possible to verify manufacture date? Something like JS0910XXXXXXX - thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

0 Likes
0
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

Thanks for your reply Angela.

I imagine that's what happend, 72 hours without any power whatsoever.

manufacturing date is 25 of august 2012 according to the warranty check. (message below)

Your APC Smart-UPS RT 2000VA 230V (SURT2000XLI) comes
standard with a 2 years repair or replace, optional on-site warranties
available, optional extended warranties available
factory warranty. The
warranty is effective from the date of purchase. In the event that you are not
able to locate a dated proof of purchase receipt, your warranty is effective
from the product's manufacture date. Your product was manufactured on August
25, 2012
.


Or is this completely different ? If so I'll send the serial nr.

Greetings,

Kevin

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

0 Likes
0
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:47 AM . Last Modified: ‎2024-03-13 12:29 AM

Yes that information will do as well. Just wanted to see how old the batteries would be as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:48 AM . Last Modified: ‎2024-03-13 12:29 AM

0 Likes
0
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:48 AM . Last Modified: ‎2024-03-13 12:29 AM

Ok, so 1 last question. Is it possible to extend the sleep time for this model ? I've had a quick look in the powerchute software but didn't see any option that would refer to the sleeping time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:48 AM . Last Modified: ‎2024-03-13 12:29 AM

0 Likes
0
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:48 AM . Last Modified: ‎2024-03-13 12:29 AM

You can only change the sleep time when you are commanding it to sleep for a particular amount of time - you cannot adjust anything like that for a low battery shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore