UPS not providing battery power

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS not providing battery power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:33 AM

0 Likes
8
6859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:33 AM

UPS not providing battery power

Hi, All--

I have a SU2200NET that I acquired several years ago, and until recently, it has worked perfectly and saved my "bacon" several times.

On January 29th, for some reason, my machines went down while I was away; I also have a 9617 network management card installed in it, so I checked the log to see what had happened, but there was nothing definitive in there--it just indicated that "the output power is turned off"

Thinking that there might be a problem with the firmware on the card, I upgraded it to the latest 3.5.5 firmware

After the firmware upgrade, the logs now state the following:

*********************************************************************************************************************************************************************************
01/29/2008 11:49:05 UPS: The output power is now turned on.
01/29/2008 11:49:02 UPS: A discharged battery condition no longer exists.
01/29/2008 11:49:01 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
01/29/2008 11:49:00 UPS: The output power is turned off.
*********************************************************************************************************************************************************************************

The battery showed 100%, so I couldn't figure out what could have caused the UPS to not provide battery power.

Yesterday evening, there was a quick spike/surge, and my machines went down AGAIN . . . this time, the logs displayed the following:

*********************************************************************************************************************************************************************************
02/15/2008 21:08:50 UPS: A discharged battery condition no longer exists.
02/15/2008 21:03:37 UPS: The output power is now turned on.
02/15/2008 21:03:36 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
02/15/2008 21:03:34 UPS: The output power is turned off.
*********************************************************************************************************************************************************************************
To my eye, the logs look pretty much identical; I obtained this log when I got my machines booted back up, and when I went into the UPS "Overview", it looked like the battery was dead--it was charging, but it was at around 1%, and through the evening, I could see it climbing slowly. This morning, it was displaying back at 100%.

Every time I have viewed the status previous to this event, it always showed the battery at 100%, as it does now. It's also showing a load of only 23.4% (about 375w).

This morning, I performed a "self test", and when I clicked on that link, the UPS shut off AGAIN!

This was in the logs after I got the machines back up:

*********************************************************************************************************************************************************************************
02/16/2008 05:42:45 UPS: Restored the local network management interface-to-UPS communication.
02/16/2008 05:42:21 System: Network service started. System IP is x.x.x.x from manually configured settings.
02/16/2008 05:42:21 System: Coldstart.
*********************************************************************************************************************************************************************************

I edited the IP address in the log, just for security purposes.

Now, my question is this--why would it suddenly shut down, or what could be causing it to be discharged when power is lost? Are my batteries bad? Is there maybe a problem with the UPS itself?

Any assistance with this would be greatly appreciated . . .

Thanks in advance!!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • hardware
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:08 AM . Last Modified: β€Ž2024-03-08 01:32 AM

0 Likes
0
6858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:08 AM . Last Modified: β€Ž2024-03-08 01:32 AM

If you pull the plug what happens

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:33 AM

0 Likes
0
6858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:33 AM

Hello,

There is one of two things wrong with the UPS:

1. If the UPS immediately powers off and doesn't go to battery, there is a relay failure and the UPS would have to be repaired/replaced.

2. If the UPS goes to battery, even for a second, the battery is discharged, however, if it's a new battery, and exhibits the same thing, then there is a problem with the battery charger, which would have failed, causing the UPS to THINK the battery is charging, when in actuality, it's likely discharging the battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:33 AM

0 Likes
0
6858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:33 AM

Thanks for the reply--the UPS doesn't have a new battery pack, they're probably 3 or 4 years old, but I'm not sure if it's really charging the batteries or not; is there some safe way I can test them without dumping my machines again?

If it isn't the batteries, it DOES behave as if there is a problem with the relay, so do you happen to know who would have the part and/or who might repair the unit?

Again, thanks for your help!

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:32 AM

0 Likes
0
6858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:32 AM

If you have any type of multimeter, you can take it to the batteries. Decent batteries will float at a full charge on a 2200 around 27.4 VDC per set, as that's how you'll have to read the RBC11.

If the UPS needs to be repaired, APC's only authorized repair service is Coastal Business Machines (1-888-234-9877).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:32 AM

0 Likes
0
6858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:32 AM

Quote The Notorious K.M.P.

1. If the UPS immediately powers off and doesn't go to battery, there is a relay failure and the UPS would have to be repaired/replaced.

UnQuote

Your post about the relay just go me thinking, I was experiencing a problem with my UPS, the unit would not send out power upon mains loss. So after reading you comment about a relay and having quite a good knowledge on how a relay works I opened up the unit (removing the battery first of course) and gave the white relay inside a little tap with a screwdriver. I figured they are not switching over to battery power on mains loss. Reassembling the unit, i attached a device cord and noticed an instant noise/feel from within the UPS and eureka, it worked! Thanks for the tip πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:32 AM

0 Likes
0
6858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:07 AM . Last Modified: β€Ž2024-03-08 01:32 AM

Old thread, but same problem

Using the management card and a MIB browser I can see that the voltage reported by the system is 27.6V, so that would match the charging volts indicated here.

Can I trust that value to tell me that the charger is working fine?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:08 AM . Last Modified: β€Ž2024-03-08 01:32 AM

0 Likes
0
6858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:08 AM . Last Modified: β€Ž2024-03-08 01:32 AM

What Is The Model And Serial Number Of The Ups

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:08 AM . Last Modified: β€Ž2024-03-08 01:32 AM

0 Likes
0
6858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:08 AM . Last Modified: β€Ž2024-03-08 01:32 AM

SU1400RM12U
AS0222110197

Mick

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:08 AM . Last Modified: β€Ž2024-03-08 01:32 AM

0 Likes
0
6859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:08 AM . Last Modified: β€Ž2024-03-08 01:32 AM

If you pull the plug what happens

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore