UPS not powering off after shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS not powering off after shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
RaBu78
RaBu78
Cadet

Posted: ‎2024-06-13 12:42 AM

0 Likes
4
639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-13 12:42 AM

UPS not powering off after shutdown

Dear all,

 

we have a racked Smart-UPS SRT 5000 and we execute every year a Power Failure test to check if all servers will shutdown correctly aso. After the shutdown the UPS should power off. The last years it works without any problems but not this year. That means all servers are shutdown correctly but the UPS is running and not powering off.

 

We didn't change the configuration, the firmware or the software version. It is exactly the same like in the other years. We only replaced the battery before the test but I think this cannot be the reason.

 

Here is the protocol from 2023:

image.png

 

And this is the protocol from 2024 - There is no event "UPS Outlet Group: Servers turn off has been initiated" 

image.png

 

Here is our configuration:

image.pngimage.pngimage.pngimage.png

 

Does anybody knows what is wrong?

 

 

Best regards


Rainer

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2024-06-14 05:51 AM

0 Likes
3
582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-14 05:51 AM

@RaBu78 

 

From the screenshot, I can see that at 20:01:51, PowerChute recorded shutting down UPS 10.0.1.170. This means PowerChute sent the shutdown command to the UPS. You should check the NMC event log to see if the command was received. If it had not been received or received, and PowerChute did not receive the follow-up, it could have been a network issue. 

 

I suggest rebooting the NMC and restarting the PowerChute service. 

 

Note:

You could configure load shedding on the NMC, and that would trigger the PowerChute shutdown. Then the NMC will then command the UPS off. If you do configure load shedding you must deselect "Skip outlet off delay."

 

Reply

Link copied. Please paste this link to share this article on your social media post.

RaBu78
RaBu78
Cadet

Posted: ‎2024-06-17 03:41 AM

In response to BillP
0 Likes
2
535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-17 03:41 AM

@BillP

 

thanks for your feedback. I'm missing the log-entry "UPS Outlet Group: Servers turn off has been initiated". I think that is the reason why the power off is not triggered. There are no communication issues during the power off test between the Power Chute Agent and the UPS.

 

I rebooted the NCM. The PowerChute service was restart with the start of the server after the power off test.

 

 

If I use load shedding what do I need to do. I want the flowwing workflow:

 

1. If Power off occur wait 60 seconds. 

2. If  > 60 seconds start shutdown (script)

3. After 540 seconds (9 Minutes) shutdown the UPS.

 

That means from start power off until shutdown UPS the overall time is 10 minutes.

 

I would change the follwing:

1.jpg

 

Is this correct?

 

 

2.jpg

If I use load sheeding should I disable this shutdown event because (I think) this would be done by NCM. As you said NCM should trigger PowerChute.

 

3.jpg

 

If I use load sheeding should I change this option to "Do not turn off the UPS" because this is done by load shedding?

 

 

Thank you!

 

Best regards

Rainer

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2024-06-17 08:03 AM

In response to RaBu78
0 Likes
1
526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-17 08:03 AM

Hi,

 

If you are switching to load shedding, you should disable the UPS on battery event in the PowerChute UI and disable UPS turn-off. You must also enable load shedding for each outlet group to allow the UPS to power off before the battery is drained.  

 

When PCNS receives the UPS/outlet group turn-off signal from the NMC, it will trigger the shutdown. The command file will be run, and then the OS will be commanded off. 

Reply

Link copied. Please paste this link to share this article on your social media post.

RaBu78
RaBu78
Cadet

Posted: ‎2024-06-18 12:14 AM

In response to BillP
0 Likes
0
503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-18 12:14 AM

Hi,

 

ok, as far as i understood - My configuration in the screenshot seems to be correct!? Or did I forget something?

 

 

Best regards


Rainer

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of