Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

UPS needs for small scale server room

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS needs for small scale server room
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:16 AM . Last Modified: ‎2024-03-14 12:55 AM

0 Likes
3
926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:16 AM . Last Modified: ‎2024-03-14 12:55 AM

UPS needs for small scale server room

Hi there, I need a new UPS for a small scale server room, I was hoping some of you might be able to help narrow down my needs. Basically put I have the following I would like to run off the UPS: NAS(150W), Firewall(100W), DSL Model (18W), Switch (160-384W), I will also be adding a server shortly(500-750W) so about 1152 - 1402 Watts total, it has to be rack moutable, and all my devices use Nema 5-15P, I do not plan any more upgrades in the near future. Hopefully I did the formulas right!

Anyways I have it narrowed down to the following:

SMX1500RM2U, this will meet the lower end wattage requirements, but not the higher ones, so my server choice would be limited, but this one is also listed as compatible to my QNAP TS-439U-SP NAS, but I assume this only makes a difference if I was using the NAS for UPS management? Also most cost effective choice.

SUM1500RMXL2U, this will meet both needs for wattage, and also has a RJ45 jack for network management which seems to be a plus, also seems to have more "bells and whistles" but slightly more money that the SUA2200RM2U which has more power

SUA2200RM2U, this will meet all my needs, but seems to be an older model? Are the Nema 5-20P out plugs compatible with the 5-15P input? it seems they are 5-15/5-20

Anyways based on what I am looking to do, do any of these stand out to you as the choice for my setup?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:17 AM . Last Modified: ‎2024-03-14 12:55 AM

0 Likes
0
926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:17 AM . Last Modified: ‎2024-03-14 12:55 AM

Hi there, I need a new UPS for a small scale server room, I was hoping some of you might be able to help narrow down my needs. Basically put I have the following I would like to run off the UPS: NAS(150W), Firewall(100W), DSL Model (18W), Switch (160-384W), I will also be adding a server shortly(500-750W) so about 1152 - 1402 Watts total, it has to be rack moutable, and all my devices use Nema 5-15P, I do not plan any more upgrades in the near future. Hopefully I did the formulas right!

Anyways I have it narrowed down to the following:

SMX1500RM2U, this will meet the lower end wattage requirements, but not the higher ones, so my server choice would be limited, but this one is also listed as compatible to my QNAP TS-439U-SP NAS, but I assume this only makes a difference if I was using the NAS for UPS management? Also most cost effective choice.

SUM1500RMXL2U, this will meet both needs for wattage, and also has a RJ45 jack for network management which seems to be a plus, also seems to have more "bells and whistles" but slightly more money that the SUA2200RM2U which has more power

SUA2200RM2U, this will meet all my needs, but seems to be an older model? Are the Nema 5-20P out plugs compatible with the 5-15P input? it seems they are 5-15/5-20

Anyways based on what I am looking to do, do any of these stand out to you as the choice for my setup?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:16 AM . Last Modified: ‎2024-03-14 12:55 AM

0 Likes
0
926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:16 AM . Last Modified: ‎2024-03-14 12:55 AM

thanks for your response, helps clear up a few things! So from looking at this I believe the SUA2200RM2U is the unit for me, even if its a bit older, from my calculations I should be able to have everything in the wiring closet run off the one UPS which is nice, and also leaves me some room for future considerations. In the end this is more important to me than network connectivity, which from my understanding I can also add a card into this unit if I wanted to go that way down the road.

Will this connect to my NAS through USB I wonder? or will it have to be configured off a termporary workstation, or a really long USB cord I plug into the closet until I get the server?

Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:17 AM . Last Modified: ‎2024-03-14 12:55 AM

0 Likes
0
926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:17 AM . Last Modified: ‎2024-03-14 12:55 AM

Yes, you can definitely add a network card down the line if you wanted to.

I think your NAS might have native support for use with a UPS, though I'd double check on yours to be sure. If so, it could probably communicate over USB like you said.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:17 AM . Last Modified: ‎2024-03-14 12:55 AM

0 Likes
0
927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:17 AM . Last Modified: ‎2024-03-14 12:55 AM

Hi there, I need a new UPS for a small scale server room, I was hoping some of you might be able to help narrow down my needs. Basically put I have the following I would like to run off the UPS: NAS(150W), Firewall(100W), DSL Model (18W), Switch (160-384W), I will also be adding a server shortly(500-750W) so about 1152 - 1402 Watts total, it has to be rack moutable, and all my devices use Nema 5-15P, I do not plan any more upgrades in the near future. Hopefully I did the formulas right!

Anyways I have it narrowed down to the following:

SMX1500RM2U, this will meet the lower end wattage requirements, but not the higher ones, so my server choice would be limited, but this one is also listed as compatible to my QNAP TS-439U-SP NAS, but I assume this only makes a difference if I was using the NAS for UPS management? Also most cost effective choice.

SUM1500RMXL2U, this will meet both needs for wattage, and also has a RJ45 jack for network management which seems to be a plus, also seems to have more "bells and whistles" but slightly more money that the SUA2200RM2U which has more power

SUA2200RM2U, this will meet all my needs, but seems to be an older model? Are the Nema 5-20P out plugs compatible with the 5-15P input? it seems they are 5-15/5-20

Anyways based on what I am looking to do, do any of these stand out to you as the choice for my setup?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore