Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
UPS for small business?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-1808:26 AM. Last Modified: 2021-11-2406:36 AM
UPS for small business?
currently we have the following hardware in our rack:
2 x Dell Poweredge R430
Synology RS3617xs+
Sophos UTM
small Dell PowerConnect Switch
HP ProLiant Octacore something
speed testWhats still missing is an Uninterruptible Power Supply. What would be an appropriate UPS to power these devices plus maybe one or two more R430s? showbox
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-2201:58 PM
I usually allocate one Smart-UPS 1000 (2U) with a Network Management Card to support each server along with some ancillary equipment. This provides the longest run time during a power outage. If I wasn't being conservative, I'd double the number of servers.
Based on your current configuration, that'd be three devices, which also allows for your anticipated growth pattern.