UPS detected in Device Manager but Cannot Discover the device in Business Edition Deluxe Software

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS detected in Device Manager but Cannot Discover the device in Business Edition Deluxe Software
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:23 PM . Last Modified: ‎2024-03-06 11:04 PM

0 Likes
8
1758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:23 PM . Last Modified: ‎2024-03-06 11:04 PM

UPS detected in Device Manager but Cannot Discover the device in Business Edition Deluxe Software

Hi There,

We have plugged in USB Cable from APC USB UPS to server and we can see it installed in Device Manager as shown in Image below.

But when we are trying to Add the device to APC PowerChute Business Edition Deluxe Software it is not showing that Device.

Can I please get some suggestion re this.

Device Manager

Thanks,

Jatin

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • ups
  • usb
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:03 PM

0 Likes
0
1757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:03 PM

I think the HID UPS Battery in the device manager should update to an APC version with the software, you may be able to right click and update manually, then untick the show compatible hardware to see if the APC option is there, click that and then powerchute will detect it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:23 PM . Last Modified: ‎2024-03-06 11:04 PM

0 Likes
0
1757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:23 PM . Last Modified: ‎2024-03-06 11:04 PM

Hi,

Is the UPS not being discovered by the PowerChute Server and Console or is the UPS not being discovered when you attempt to install the PowerChute Agent? Also, What model Smart-UPS are you attempting to communicate with?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

0 Likes
0
1757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

Hi Bill,

Yes it is not getting discovered by the server and console.

Model: APC Smart-Ups 750

Thanks,

Jatin

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

0 Likes
0
1757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

Hi,

Can you log into the PowerChute Agent web interface and if so does the web interface show that the UPS and the Agent are communicating? To log into the Agent web interface open a web browser (Internet Explore, Firefox, Chrome) and enter https://:6547. If the Agent and UPS are communicating then in most cases the communications issue between the Agent and PowerChute Server is due to a mismatch in the user name and password. When installing the Agent and the PowerChute Server you are asked to enter a user name and password. Those must match for the Agent and PowerChute Server to communicate. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

0 Likes
0
1756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

Thanks Bill for quick response.

I had a look at web interface and it shows as below:

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

0 Likes
0
1757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

Hi,

The PowerChute Server is not discovering the Agent because there is a communication error between the Agent and the UPS. What is the model and Serial numbers of the UPS and what version of PowerChute Agent, Server, and Console are installed? Also, What communications cable is attached between the UPS and computer?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

0 Likes
0
1756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

Hi Bill,

Details as below:

  • UPS Model: APC Smart-UPS 750
  • Communication: Powerchute via USB
  • APC PowerChute Business Edition Console 9.0 Build 613

Thanks,

Jatin

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

0 Likes
0
1757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:04 PM

Hi,

Uninstall the PowerChute Agent and then reinstall. When installing verify that the UPS is discovered by the installer. Once the Agent is reinstall log into the Agent web interface to verify communication is established. If communication has been established open the Console and add the Agent to the PowerChute Server.

NOTE: When installing the Agent be sure to use the same user name and password and used with the PowerChute Server.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:03 PM

0 Likes
0
1758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:24 PM . Last Modified: ‎2024-03-06 11:03 PM

I think the HID UPS Battery in the device manager should update to an APC version with the software, you may be able to right click and update manually, then untick the show compatible hardware to see if the APC option is there, click that and then powerchute will detect it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of