Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
UPS: Violates the InfraStruXure Manager global device battery-age threshold
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0104:57 AM. Last Modified: 2024-03-0501:53 AM
UPS: Violates the InfraStruXure Manager global device battery-age threshold
I recently started getting this alert from my InfraStruxure Manager. I am on a very old system version 4.7
The UPS itself is over 9 years old, the threshold has been set to the default 60 months for some time and the alerts just started. If I change the Global Thresholds to 62 months or more the warning goes away. Is this particular threshold a level for any one of the batteries in the unit? ie, the oldest if finds? I have a Symmetra 20K system.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0104:57 AM. Last Modified: 2024-03-0501:53 AM
This global threshold would apply to all the devices the ISX Manager is monitoring. It then should tell you what device(s) violate the threshold. I think for this UPS, it's going by the last battery replacement date that is set in the Symmetra's management card. As far as I know, there is only one date you can set on the UPSs regardless of how many battery modules the device has. In general, all batteries in most UPSs should all be the same age and replaced at the same time.
If you log into the device, it sounds like the batteries haven't actually failed yet (and you could double check) but if they are this old, then it might be time to start budgeting for new batteries on the system because they could need replacement soon based on their age.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0104:57 AM. Last Modified: 2024-03-0501:53 AM
This global threshold would apply to all the devices the ISX Manager is monitoring. It then should tell you what device(s) violate the threshold. I think for this UPS, it's going by the last battery replacement date that is set in the Symmetra's management card. As far as I know, there is only one date you can set on the UPSs regardless of how many battery modules the device has. In general, all batteries in most UPSs should all be the same age and replaced at the same time.
If you log into the device, it sounds like the batteries haven't actually failed yet (and you could double check) but if they are this old, then it might be time to start budgeting for new batteries on the system because they could need replacement soon based on their age.