UPS: On battery power in response to an input power problem - details?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: On battery power in response to an input power problem - details?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

0 Likes
4
11238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

UPS: On battery power in response to an input power problem - details?

Hi,

We have several UPS-systems which give an error 'UPS: On battery power in response to an input power problem', luckely followed very soon (eg 1 second later) by the information that the problem is solved (every day there is at least one of the UPS giving this error, but mostly there are more).  The messages as such aren't a big problem, the fact that the UPS switches cause more issues.

When I look at the data-logs of the UPS, I don't see what could have caused this (at least no over- or undervoltage), but there must be a reason I guess as it's more than one system giving this error, not at the same time however (they aren't all connected to the same power line either).  The most positive idea would be there is a fireware issue, but I guess this would be too much positive thinking smile

However, it's not just an issue of alerting, still could be UPS-firmware however, or the sensors, but some of the equipment "protected" by the UPS can give an alert as well of a short power failure when the UPS switches...

Is there an option to get information of the UPS on what specific parameter he gave this error?  Or even just an overview on which parameters that can cause this specific error?  I'd like to test this with other equipment as well, but if we could trigger on the reason the UPS think it should react too, it would be easier.

The used UPS are Smart-UPS 3000 RM, this weekend 4 of the 7 UPS (of that type) gave errors like this (most of them multiple times par day).

Thanks in advance,

Alain

Attachments
event.txt.zip
data.txt.zip
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

0 Likes
0
11236
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

Hello.

I tracked down a newer SMX UPS that supports this with v5.1.7 on its network management card and I do not see these last 10 transfer reasons there after double checking. You'd have to upgrade to v6.2.0 Smart-UPS application (sumx) Network Management Card firmware (as you suggested might need to happen) which in there, it is under Logs->UPS logs.You could also view it through the LCD on the UPS (as long as it is in advanced mode). v6 firmware just had a new release which fixed a lot of existing issues and has many new features if you're still on v5. There may be some devices on testdrive.apc.com with this firmware already so you can see it before you upgrade.

Regarding your question on sensitivity, since we are in the business of providing power protection, we always want to deliver the highest possible quality power for our customers. That means, that by default we set to High, which is very, very strict. Even at our very lowest/widest settings, we will never let anything through that could possibly risk anything to the equipment. The only issue with sensitivity is that the lower the setting, the longer the transfer time.

Let me know if you have further questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

0 Likes
0
11236
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

For this UPS, unfortunately, we really only have the event and data log from the Network Management Card itself to go off of. It is likely the data log is not catching the particular thing that is causing this and the UPS is seeing something really obvious to the naked eye causing it to transfer to battery. For example, a rapid change in voltage over time, over the span of a few seconds, is not likely to be reported with the Network Management Card. The UPS (this model anyway) only has the capability to tell the Network Management Card a few select things. Or, a frequency problem could be an issue. The Network Management Card can only  provide a snapshot of the frequency at the time it logs the data log since neither the UPS nor the Network Management Card can store min/max frequency like the UPS can with the voltage.

Here is a general article on reasons why a UPS goes to battery -> Reasons a Smart-UPS Will Transfer to Battery | FAQs | Schneider Electric US

Anyway, my first thought is to ask what is the sensitivity set to on your UPS? We can try bumping it down a notch to see what happens so that the UPS is less sensitive to tiny little power issues. You'd see this under UPS tab->Power Settings I believe. We also see the need for this such as when a generator is in use or if the utility power company is experiencing problems. It could also be caused by something on the same circuit causing a strange issue but that is the minority of issues.

I can tell your UPS must be the older type (well this one the logs are from anyway) without an LCD screen based on the fact you have an AP9617/18/19 model Network Management Card in it (which I can tell by the firmware version on the log files). Our newer UPSs with SMT, SMX, and SRT model prefixes have the capability on the UPS itself to record the last 10 reasons it transferred to battery. I would've had you check that so we can see what the UPS logged itself (which those UPSs work with AP9630/31 only). Are any of your UPSs the newer model with the LCDs?

Though, now that I think of it, I do believe this UPS will list the last single transfer reason under Status or Overview menu. Can you look there and see what it says?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

0 Likes
0
11236
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

Hi Angela,

Thanks for the information. I modified the sensitivity on one of the switches to low, another to reduced.  Currently all were set to high.  Let's see if this makes a difference ... Is there a risk to a "low sensitivity"?

I also found the information on the reason in the status (an old UPS mentions a "line voltage notch" ; the new one mentions "distorted input", which will probably be the same).  On the more recent UPS (we have 3 with LED display, so 10 in total), I didn't find the history of "10 reasons" like you mention, but the firmware might not be the most recent one either.  Do I need to activate this 'history' in some way?  Or is this a firmware thing (aos/sumx is version 5.1.7 from late 2011) ; I prefer not to upgrade when there is no real need ... I did this for the network cards on the older equipment just to get them the same however, but not on the newer systems.

Thanks,

Alain

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

0 Likes
0
11237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

Hello.

I tracked down a newer SMX UPS that supports this with v5.1.7 on its network management card and I do not see these last 10 transfer reasons there after double checking. You'd have to upgrade to v6.2.0 Smart-UPS application (sumx) Network Management Card firmware (as you suggested might need to happen) which in there, it is under Logs->UPS logs.You could also view it through the LCD on the UPS (as long as it is in advanced mode). v6 firmware just had a new release which fixed a lot of existing issues and has many new features if you're still on v5. There may be some devices on testdrive.apc.com with this firmware already so you can see it before you upgrade.

Regarding your question on sensitivity, since we are in the business of providing power protection, we always want to deliver the highest possible quality power for our customers. That means, that by default we set to High, which is very, very strict. Even at our very lowest/widest settings, we will never let anything through that could possibly risk anything to the equipment. The only issue with sensitivity is that the lower the setting, the longer the transfer time.

Let me know if you have further questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

0 Likes
0
11236
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:39 AM . Last Modified: ‎2024-03-12 02:54 AM

Hi Angela,

Thanks for all the info!  At the moment I don't have the time for the update, but I'll try to schedule this in a few weeks/months (depending on other priorities).

BR,

Alain

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore