UPS NMC Firmware Upgrade Problems

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS NMC Firmware Upgrade Problems
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
10
3500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

UPS NMC Firmware Upgrade Problems

I am having a problem upgrading the firmware on an AP9606 fitted in a Smart-UPS 1500 RM. Old firmware was AOS 3.2.1 and APP sumx 3.2.1. I am trying to upgrade to AOS 3.2.6b and APP sumx 3.2.6a. I have upgraded many of these units without an issue.

Using the upgrade program, I have installed both bits of firmware successfully on the device. However, the old AOS file is still present on the unit and it is this file, and not the new file that it is booting from.

I have also tired the ftp solution for upgrading but this still does not remove the old AOS. I have also reset the unit to defaults in case it was a config setting that was preventing the new AOS from loading.

How do I remove the old AOS or set the unit to boot from the new AOS file ??

Many thanks for any assistance.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • aos
  • ap9606
  • boot
  • firmware
  • NMC
  • sumx
  • upgrade
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
3500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

I don't know if you can do it but have you tried the del command for one of the bin files via FTP? I have a feeling it will not work.

Otherwise, we need to find out what AOS is currently active (v3.2.1 you see when you log in you said?) and load the old 3.2.1 APP that goes with that and hopefully get it to where it was and then retry the upgrade via FTP to be safe to the new versions.

The old sumx 3.2.1 is here -> ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/sumx/v321/

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
3501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

I don't know if you can do it but have you tried the del command for one of the bin files via FTP? I have a feeling it will not work.

Otherwise, we need to find out what AOS is currently active (v3.2.1 you see when you log in you said?) and load the old 3.2.1 APP that goes with that and hopefully get it to where it was and then retry the upgrade via FTP to be safe to the new versions.

The old sumx 3.2.1 is here -> ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/sumx/v321/

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
3500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

Thanks. Will give it a try tomorrow when i'm back in work. Some have gone through without a problem, even using the upgrade program so I don't think it's the case that there's an AOS you have to upgrade to first before installing 3.2.6. I've been updating the firmware in the hope that it improves my SNMP performance but i'm not having much luck. I have a program that polls SNMP but it seems that the APC kit, in particular the NMCs in UPSs takes a long time to respond which in itself is being flagged up by the SNMP monitoring software as a network issue. Ping times are typically 70ms to 80ms while SNMP responses can take up to 1500ms. Reading in a few forums, I'm thinking the problem is the hardware and that i'm going to have to upgrade to NMC2s if the old UPSs and Masterswitches I have will support them.

Thanks for your ongoing support and will let you know how I get on tomorrow.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
3500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

Oh and I was also hoping that newer firmware would give me NTP support but that's not the case either.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

0 Likes
0
3500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:22 AM

Nope, AP9606 is ancient. NMC1 and NMC2 support NTP. We don't hear many SNMP connectivity issues with those devices. Masterswitches definitely will not support NMC2 but Smart UPS will. Most Masterswitches use AP9606 but a select few will work with AP9617 NMC1.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:21 AM

0 Likes
0
3500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:21 AM

I don't know how you do it and I don't really want to know but put sumx321 back on, then tried an ftp update of both AOS and APP and it's worked.

Think i'm going to steer clear of the upgrade program and do everything ftp from now. It seems much more reliable.

Many thanks once again for your assistance and enjoy your holiday.


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:21 AM

0 Likes
0
3500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:21 AM

Ah you know me so well. Many thanks yet again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:21 AM

0 Likes
0
3500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:21 AM

wink you're welcome

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:21 AM

0 Likes
0
3500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:21 AM

You won't find sumx 3.5.5 on the website because its older so it's been taken off. I'll attach the bin file here for you assuming you're fixing another card.

Attachments
apc_hw02_sumx_355.bin.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:21 AM

0 Likes
1
3500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:22 AM . Last Modified: ‎2024-03-05 02:21 AM

One last thing, where can I find sumx v3.5.5 for a AP9617 in a Smart UPS ??

Sorry but I find your support site very hard to use with respect to finding firmware, both old and new, for specific cards.


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-10-25 08:19 AM

In response to Anonymous user
0 Likes
0
3373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-25 08:19 AM

It is now 8 years since this thread was posted and all I can add is that the website download pages have apparently not been improved since.  The filters are not fit for purpose.  I also find that ftp is the only reliable way to go.  Hope you solved your problems.

Regards,

Budgie

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore