UPS: Compensating for a low input voltage - Bit confused!!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: Compensating for a low input voltage - Bit confused!!
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:47 AM

0 Likes
7
11002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:47 AM

UPS: Compensating for a low input voltage - Bit confused!!

Hi I hope someone can help, we have 4 APC ups's in our server room.

2 x SUA3000RMI2U (one of which has a management card installed)
2 x SU3000Inet (tower)

We've load balanced them between our servers and the load is minimal on all of them.

Late on Monday night we had a powercut, it lasted a couple of hours. When I got into the server room the next day power had been restored the and ups's were all fine (I mention this for information - it may not be related to my query)

Today (wednesday morning) I have just recived notice from my UPS with the management card that the 'UPS: Compensating for a low input voltage'

+"13.06.2012 09:02:14 UPS: No longer compensating for a low input voltage.+
+13.06.2012 08:55:02 UPS: Compensating for a low input voltage.+
+13.06.2012 08:54:53 UPS: No longer compensating for a low input voltage.+
+13.06.2012 08:38:54 UPS: Compensating for a low input voltage."+

Upon looking at the UPS's the two SUA3000RMI2U both have the low voltage light lit the two SU3000INET's don't.

I'm unsure how to tackle the problem we've used these units for years without issue, the only way i've managed to stop the notifications is to lower the threshold but its not really a solution. Should I be concerned by this?

Any help or info appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • compensating
  • su3000low
  • sua3000
  • voltage
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

0 Likes
0
10997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

Thank you for helping me with this. Yes they're 230.

I've attached the logs as requested.

See Answer In Context

Attachments
event.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:47 AM

0 Likes
0
10997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:47 AM

the different types of units you have are on different hardware platforms and firmware platforms - thus they may have difference voltage or sensitivity settings set which is causing one UPS to see the input voltage as a little low below threshold and the other one does not see the same thing.

i'd first check the device with the network management card and analyze the data log at the time the events are reported - what is the actual input voltage? ultimately you'd need to find out with an electrician or someone who can help determine what has happened to your incoming voltage to address the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:47 AM

0 Likes
0
10997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:47 AM

Many thanks for the reply,

I'm not sure if the low voltage was fluctuating somewhat but it seemed that when ever I checked the voltage was at roughly 211VAC and the threshold was set to 208VAC

When I altered the notification threshold to 204 the error stopped and the light is now clear on the UPS.

However the other identical until still has the light on which suggests to me that the input is still low. (I have no management card or powerchute install to check the readings on this unit) I assume if the power goes backup then the light should go out?

I've now re-set the threshold on the managed ups back to 208 to see if it starts complaining again.


Edit : straight away i'm notified of the low input yet the unit shows 210. Threshold is 208 ......


Message was edited by: ittim

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

0 Likes
0
10997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

this might help too depending on whats been happening.. http://nam-en.apc.com/app/answers/detail/a_id/715

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

0 Likes
0
10997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

Thank you, I'm not entirely sure I understand the table but i'm not getting anywhere near those voltages as far as I can tell.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

0 Likes
0
10997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

i was thinking that maybe the UPS is implying a hysteresis type thing where it wont come back online unless it goes back up to a certain voltage value - to avoid teetering on and off from AVR boost to online.

can you give me all of the logs to review (instructions here|http://nam-en.apc.com/app/answers/detail/a_id/9321]? these are 230v nominal voltage units, correct? i am saying that based on the model numbers you provided.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

0 Likes
0
10997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

I've just arrived into the office this morning to find that all my UPS's are now happy.

I'm wondering if the Electricity board were doing something which caused the errors.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

0 Likes
0
10998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:14 AM . Last Modified: ‎2024-03-11 02:46 AM

Thank you for helping me with this. Yes they're 230.

I've attached the logs as requested.

Attachments
event.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of