UPS: Bypass not in range ; distorted waveform.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: Bypass not in range ; distorted waveform.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-18 01:01 AM

1 Like
3
10250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-18 01:01 AM

UPS: Bypass not in range ; distorted waveform.

Installed SRT2200 a little over 1 month ago.  Every time it goes on battery I get a critical error:  Bypass not in range; distorted waveform.  Why am I getting this error message?  Whats going on?  I have attached log file. 

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-18 01:01 AM

0 Likes
0
10242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-18 01:01 AM

Hi Suzanne,

That error message is normal for your UPS during a power failure.

Bypass means feeding power to your devices directly from the utility input and bypassing the UPS. When utility power is good, the UPS might do this if it detects a hardware problem with the UPS circuitry or if commanded to do so. During a power failure, the utility input is bad (bypass out of range) so the UPS will not go into bypass.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-18 01:00 AM

0 Likes
0
10242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-18 01:00 AM

Hello 

i got that message while my power is still on

what can be the issue ?

br 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-18 01:01 AM

0 Likes
0
10243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-18 01:01 AM

Hi Suzanne,

That error message is normal for your UPS during a power failure.

Bypass means feeding power to your devices directly from the utility input and bypassing the UPS. When utility power is good, the UPS might do this if it detects a hardware problem with the UPS circuitry or if commanded to do so. During a power failure, the utility input is bad (bypass out of range) so the UPS will not go into bypass.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-18 01:00 AM

0 Likes
0
10243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:00 AM . Last Modified: ‎2024-03-18 01:00 AM

Hello 

i got that message while my power is still on

what can be the issue ?

br 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:01 AM . Last Modified: ‎2024-03-18 01:00 AM

0 Likes
0
10242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:01 AM . Last Modified: ‎2024-03-18 01:00 AM

Most likely the power is on but not acceptable quality Therefore the UPS will not switch to bypass -- normal UPS operation is unaffected and will clean the power via double-conversion. Your options:

- You can discuss power quality with the power provider.
- You can rely on the UPS to clean the utility power and accept that the UPS will not go to bypass.
- You can accept the quality of the utility power and attempt to loosen the frequency tolerance in the UPS power settings. I don't have an SRT2200 in front me right now to see if it has this setting.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of