I have an APC UPS 2200, plug is NEMA 5-20P, unfortunately the receptacles in the room are NEMA 5-15R, and Can I use a Nema 5-15R or Nema 5-20R to Nema 5-15P Power Plug Adapter? Will the 5 amps make a difference?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:45 AM . Last Modified: 2024-03-13 01:26 AM
A 5-20 plug will not plug into a 5-15 receptacle. You could use a plug converter but the UPS would be limited to 15amps. In that case, the UPS would be derated, essentially to a 1500VA UPS
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:45 AM . Last Modified: 2024-03-13 01:26 AM
A 5-20 plug will not plug into a 5-15 receptacle. You could use a plug converter but the UPS would be limited to 15amps. In that case, the UPS would be derated, essentially to a 1500VA UPS