Two questions re: PowerChute Network Shutdown in VMWare enviornment

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Two questions re: PowerChute Network Shutdown in VMWare enviornment
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:35 AM

0 Likes
13
2646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:35 AM

Two questions re: PowerChute Network Shutdown in VMWare enviornment

Hello,

I am just starting to connect a Smart-UPS 2200 to our recently migrated and P2Ved ESX  5.1 environment.  All of my servers are now VMs  running in ESX 5.1.

I've been reading the PDF  for PCNS  when working with virtual environment and have two questions:

1. The PDF  indicates that I should install PCNS  on a physical Windows host when dealing with one ESX  host in which all servers exist on that host. All that I have, however, are workstations that aren't guaranteed to be up continuously. Is there any major drawback to skipping the physical WIndows  host suggestion?

2. I see reference to a vCenter  Plug-In, but cannot find the download. Where is that?

Cheers,

Mike Whalen

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • esxi
  • network-management-card
  • pcns
  • PowerChute
  • powerchute-network-shutdown
  • shutdown
  • smart-ups
  • vmware
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:32 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:32 AM

Andy,

Ultimately the last message I wrote was the key. I had to configure PCNS to only work with the ESX host, not vCenter. I then had to configured the startup/shutdown settings in ESX and make sure that VMs that depended on other VMs came up (or went down) in the proper order.

My situation may be different from yours, though. I was dealing with a single host that ran VCenter AND the PCNS virtual appliance on the ESX same host. Unless I mis-read your email, you have a different situation.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 13
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:35 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:35 AM

I've installed the Windows PCNS 3.1 on the main server (VM). It asked me for VMWare  Support, which I checked because I do want that.

But now I wonder if I should let PCNS  VMWare  Appliance handle that? If so, is it better to remove management duties from the Server? Is that a reinstall?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:35 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:35 AM

Mike,

I assume when you wrote VMware ESX 5.1 you mean ESXi 5.1. With ESXi 5.1 I recommend installing PCNS 3.1 appliance and have that handle the shutdown protection. PCNS 3.1 appliance is a VM running CentOS with PCNS 3.1 pre-installed so all you have to do is install the OVA file, set the network info, provide password, and then configure PCNS via the web interface. I do not recommend installing PCNS 3.1 on a Windows VM. There is a possibility that that VM could be powered down with the other VMs and therefore would not be available to power down the host.

If you are using vCenter Server you should review Application Note 180 pages 10 -13 of the PDF. This will help you understand what needs to be done to be sure that PCNS, vCenter Server and the host/s are powered down properly.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:35 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:35 AM

On 1/7/2015 8:54 AM, Bill said:

I assume when you wrote VMware ESX 5.1 you mean ESXi 5.1. With ESXi 5.1

Thanks correct. Yes.

On 1/7/2015 8:54 AM, Bill said:

I recommend installing PCNS 3.1 appliance and have that handle the shutdown protection. PCNS 3.1 appliance is a VM running CentOS with PCNS 3.1 pre-installed so all you have to do is install the OVA file, set the network info, provide password, and then configure PCNS via the web interface.

Ok. I have done that. Thanks.

Do I also need to installed PCNS  agents on any VMs? Or is the appliance all that's required?

On 1/7/2015 8:54 AM, Bill said:

I do not recommend installing PCNS 3.1 on a Windows VM.

I believe that when you say this, you're talking about installing PCNS  3.1 on a Windows VM in order to control the shutdown sequence for VMs  and host. If that's the case -- and considering what I'm reading in AN180 -- then it's beginning to sound as if I should install the PCNS  Appliance (OVA) and set up local login  for shutdowns on the ESXi  host. I should then UNINSTALL  the PCNS  installs on any other VMs. 

Correct?

Thanks for your help!

m

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

Mike,

You only need to install the PCNS appliance (OVA) and configure that. If you have PCNS installed on any other VMs it should be uninstalled. To be sure all of the VMs and host/s are powered down properly you should create local login and configured each hosts and vCenter Server with this login.

I have attached a PDF that discusses how to create a local user on a Windows VM running vCenter Server and on ESXi host/s managed by vCenter Server.

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

Ok, let me see if I understand.

1. Uninstall the PCNS  software installed on any VMs.

2. Create a LOCAL pcnsadmin  Administrator account on every VM I want to respond to a PCNS  shutdown command (Windows, Linux, whatever).

3. Create a Administrator-level account on both  my vCenter (VM) server and my ESXi  host.

4. Configure the OVA PCNS  Appliance to use pcnsadmin  to connect to vCenter.

That it?

And here's a follow up if my above steps are correct: What is there are VMs  in which I cannot make a local Administrator-level account? For instance, I have a couple of virtual appliances that will not allow me to create other users within.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

Mike,

You do not need the pcnsadmin account on each VM. It only needs to be on the host, vCenter Server, and used as the credentials that PCNS uses to connect to vCenter Server. When PCNS see that the VMs and host need to power down it will follow these steps

1 Host is put into maintenance mode

2  VMs are commend down

3  vApps are command down (if any)

4 vCenter Server is commanded down

5 Host is commanded down

6 PowerChute starts the appliance shutdown and at the same time it will send a shutdown command to the UPS to power down the outlet group or UPS if configured to do so.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:33 AM

Thank you again!

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:33 AM

Hello,

I'm afraid the first power-down test failed. And just to clear the air: This is ONE ESXi host with ONE vCenter VM Appliance on the _same_ host.

I set the On Battery shutdown command and pulled the plug. PCNS (the appliance) started to shutdown everything. However, PCNS shutdown the vCenter appliance and then complained it could not speak to vCenter.

The next test, I placed vCenter in the _last_ position on shutdown. That allowed more machines to get commanded to shut down, but still the vCenter shutdown was early and the other machines would not shut down. I can't swear that I waited 840 seconds (see below), but I am fairly certain I did.

There are five virtual machines on this ESXi host:

1. Windows Server 2012
2. Windows Server 2003
3. Dell OMSA Plug-in for vCenter
4. PowerChute Network Shutdown
5. VMWare vCenter

I have VM Shutdown in PCNS set to 120 seconds.
I have vCenter Server shutdown in PCNS set to 840 seconds, which I calculated from 120*5 + VMs + an additional 240 for ESXi host shutdown. (Again, I can't swear I waited a full 840 seconds.)

Additionally, I have to note that the Dell OMSA Vm will not respond to commands to shut it down. I don't have the ability to install VMWare Tools. I'll have to see if there's another way.

Initially, I wondered if I should reconfigure PCNS to point at the ESXi host and treat it as a standalone. In that situation, I think I would have to make sure PCNS is the last VM to shutdown. The problem is, I think, that once the PCNS appliance goes down, the ESXi host will never get a shutdown command.

Either that, or my timings are off.

Is this even a supported configuration?

Cheers,

 

m

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:33 AM

I spoke to tech support this morning. They suggested re-configuring the appliance to treat ESXi  as a standalone-host rather than vCenter-managed. I'll schedule another shutdown test.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:33 AM

Did yoy manage to get this to work.

I have a similar situation a remote site with 2 ESX hosts + UPS and this site with the vCentre server.

I've created a local account on the windows vCentre server and added within vcentre, then gone to both remote hosts and added it there.

I've tried to test by moving the vCentre off the network and testing shutting down the UPS but Powerchute complains it can't see the VC and doesn't shutdown the host.

Andy

 

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:33 AM

Andy,

What version of PowerChute are you running and is PowerChute running on a stand-alone Windows system or on a VM?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:32 AM

0 Likes
0
2645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:32 AM

version 4.1 and it is running on a physical windows 2008 box

Thanks

Andy

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:32 AM

0 Likes
0
2646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:24 PM . Last Modified: ‎2024-03-14 04:32 AM

Andy,

Ultimately the last message I wrote was the key. I had to configure PCNS to only work with the ESX host, not vCenter. I then had to configured the startup/shutdown settings in ESX and make sure that VMs that depended on other VMs came up (or went down) in the proper order.

My situation may be different from yours, though. I was dealing with a single host that ran VCenter AND the PCNS virtual appliance on the ESX same host. Unless I mis-read your email, you have a different situation.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of