Two SMX3000RMLV2U UPS's shutdown at the same time. POSITIVE DC BUS SHORT HARDWARE CIRCUIT ERROR

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Two SMX3000RMLV2U UPS's shutdown at the same time. POSITIVE DC BUS SHORT HARDWARE CIRCUIT ERROR
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:13 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
11
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:13 AM . Last Modified: ‎2024-03-15 06:01 AM

Two SMX3000RMLV2U UPS's shutdown at the same time. POSITIVE DC BUS SHORT HARDWARE CIRCUIT ERROR

Hello all, I was out at a customer site they were reporting that their entire IT equipment rack was dead. Arrived on site and noticed both UPS were flashing "Fault State: PFC" and  "Contact APC support" on the screens. The console in the event log showed POSITIVE DC BUS SHORT HARDWARE CIRCUIT ERROR. We unplugged the load, powered both units back on, and started the servers... everything came up fine. We flipped breakers off to both units, testing under load, and still fine. 

We spent thousands on redundant circuits, UPS, etc., yet both units died at the same time?  Units are not yet 3 years old.

We have 5% load on each unit.  Both are SMX3000RMLV2U purchased and installed at the same time.  Both have 1 external battery pack connected.

This event happened when the building lost power briefly for around 6 seconds.  There are other smaller 1500 and 2000VA units in this building and they were all fine.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • failure
  • redundancy
  • redundant
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

Hi Nicholas - Sending you an email to assist...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:13 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:13 AM . Last Modified: ‎2024-03-15 06:01 AM

Hi Nicholas - 

Sorry to hear about your issue. Can I ask what exactly is plugged into these units? Is there anything with dual power supplies? 

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:13 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:13 AM . Last Modified: ‎2024-03-15 06:01 AM

Yes sir - there is Cisco Switches, HP servers and some Synology Servers and some power bricks for POE from Cisco.

The Servers all have redundant power supplies and switches.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:13 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:13 AM . Last Modified: ‎2024-03-15 06:01 AM

The issue may be caused by transients from the utility source or possibly the dual cord power supplies backfeeding during transfer. If you change your configuration so that both cords from each power supply are plugged into the same UPS you may improve performance. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:13 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:13 AM . Last Modified: ‎2024-03-15 06:01 AM

You were the first person to tell us this, we have called support several times and they were not able to tell us this we worked with APC when we first ordered these units and we told them that we were using them for... Can APC issue a replacement for a different model since these are still under warranty? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

APC wants to replace the units we have today with the same units and says its a internal issue. Does this sound right or should I push for the different units? I don't want this to happen again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

Case # 58669052

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

Hi Nicholas - 

If you plug the power cords into a single UPS, you should not have an issue using the same model. Alternately, if you do decide to continue plugging into two separate units you could try disabling Green Mode via the LCD screen, which should improve your performance. 

 

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

Green mode is off - also it doesn't say anywhere in APC guides about this. Please replace the unit with the one you recommended.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

Hi Nicholas - 

Tech support can assist you with a warranty replacement. I believe you said you already opened a case. 

 

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

They sent the SMX series. Can you help them get the right series?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
1794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

Hi Nicholas - Sending you an email to assist...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of