SURT15KRMXLT vs SURT15KRMXLI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT15KRMXLT vs SURT15KRMXLI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
10
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

SURT15KRMXLT vs SURT15KRMXLI

I have an old SURT15KRMXLT that I want to use with a 240 volt, 3 phase supply. I need the output to also be the same - 240 volt, 3 phase. I can work with single phase output if 3 phase is not an option. 

Looking through documentation, the SURT15KRMXLI seems to be rated for 240 volts, 3 phase. My unit, the SURT15KRMXLT appears to be rated for 208 volts, 3 phase. What's really the difference between these units and can I use mine with the 240 volt input? I intend to hardwire both the input and output so I am not concerned with the PDU outputs of the UPS. 

Is this just a matter of starting it up and configuring settings? If so, is it safe to start up with the higher voltage if that is not already configured so? My unit is also missing the powerview controller so I will have to rely on configuring it via the NMC. Anyone know what is the part number for the powerview that will work with this unit?

Thank you for your help. 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

You can do that, but the output will be 2 unbalanced hots and a ground when you switch to battery. You will likely track the input when you are in online mode, but then revert to H/H/G on battery. This UPS is not designed for a H/N/G configuration. It is sold in North America and designed for H/H/G. The “XLI” version would be for H/N/G configurations.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:01 AM

Hi

The two ups are different.  The SURT15KRMXLT is for the North American market and has Split phase L1, L2 and G input and output wiring.  The SURT15KRMXLI is the international model and has single phase L1, N and G or 3 phase L1, L2, L3, N and G input and output wiring.

 

Regards

 

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:00 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:00 AM

Hi Matt,

Thank you for that clarification. 

I came across this FAQ article online - https://www.apc.com/us/en/faqs/FA156614/

According to this, 

There are several other Smart-UPS products that will function in a 220/230/240v environment without issue:

SURT and SURTD Units (Ex: SURTD3000XLT, SURT6000XLT, etc) - These models use a Double Conversion Online Topology that allows them to have a very wide range of  input voltages without the use of boost/trim transformers. The only change needed is to set the output voltage of the UPS to match the nominal input voltage to ensure proper output when operating in bypass mode. Output voltage can be set via a network management card or Powerchute Business Edition.

What do you make of that? Can I use my unit with a 240 volt supply? 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:00 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:14 AM . Last Modified: ‎2024-03-15 06:00 AM

Hi Matt - 

Yes, the SURT15KRMXLT can be used in nominal 208v or 240v applications, but it is only single phase in and out (Two hots and a ground). You can not feed it 3phase (Hot,Hot,Hot,Neutral,Ground). If you are feeding the UPS 240v, you should configure it to also output 240v so you wont have any issues with bypass functionality. Please note that this UPS has an unbalanced output - the output will be 240v (or 208v) from hot to hot, but it is not two balanced 120v legs. If you plan on using any 120v loads you will need a stepdown transformer. 

thanks,

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

On 5/14/2019 9:00 AM, Liam said:

but it is only single phase in and out (Two hots and a ground)

Would that be L, N and Ground for single phase 240 volt input?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

Typically in the US 240v single phase would be 120v, 120v, Ground. If the 120v are 120 degrees out of phase they would be 208v Nominal and if they are 180 degrees out of phase it would be 240v Nominal. 

If you have a single leg of 240v feeding the UPS you would connect you 240v hot to L1, Neutral to L2, and then ground to ground. The UPS will function OK with this, but remember that the output will be 2 hots and a ground with no neutral. If you need a neutral on the output you would need a stepdown transformer.

Hope this helps

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

On 5/14/2019 10:16 AM, Liam said:

Hope this helps

Certainly gives me some hope!

I don't plan to use this in the US. I want to use it in India. I have 240v 3 phase input available to me. I'm ok to use a single phase input if that's all that I can do with this unit. 

However, I need 240v output (single phase is fine, 3 phase is optional). So looking for L, N and Ground with a 240v output

On 5/14/2019 10:16 AM, Liam said:

If you need a neutral on the output you would need a stepdown transformer.

How do I get a 240v output with a stepdown transformer involved when my UPS output is also 240v? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

Hi Jay - 

 

I did a little digging. If you used the APTF20KW01 transformer and set the input switch to "200-240V" you will output 240V on terminal 10, Neutral on terminal 7, and then a ground.

You can see the wiring block I'm referring to on page 9 of the users manual:

https://www.apc.com/salestools/ASTE-6Z8LUG/ASTE-6Z8LUG_R0_EN.pdf

 

Hope this helps!

Liam

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

Thank you Liam. 

I have one more follow up question. A short while back I also chatted with APC technical support and asked them the same question. 

I was directed to this wiring diagram: https://www.apc.com/salestools/MMIS-8HZJHH/MMIS-8HZJHH_R0_EN.pdf

The agent told me to follow the wiring schematic in this document and directly use L, N and G for both input and output connections with no other hardware required. 

Do you see any problems with doing that and not using the transformer?

Edited to add transcript of chat with APC support below:

Me (5/14/2019, 11:13:56 AM): Can I setup my UPS to work with a single phase, 240v input?
Me (5/14/2019, 11:14:06 AM): And provide a single phase 240v output as well?
Dan (5/14/2019, 11:14:37 AM): SURT15KRMXLT is a single phase 240 or 208 input and output unit.
Dan (5/14/2019, 11:14:57 AM): If you need 120 volt outlets, then you would need to add a step down transformer
Me (5/14/2019, 11:15:52 AM): Don't need 120 volts output. So just hardwire L. N and G for input and out with 240 volts and that should be enough?
Dan (5/14/2019, 11:15:53 AM): it uses 3 wire for input and 3 wire for output. No Neutral.
Me (5/14/2019, 11:16:30 AM): My 240 volt supply has a live line of 240v and separate neutral and ground
Me (5/14/2019, 11:16:48 AM): so its 3 wire, L, N and G with 240v
Dan (5/14/2019, 11:17:09 AM): https://www.apc.com/salestools/MMIS-8HZJHH/MMIS-8HZJHH_R0_EN.pdf
Dan (5/14/2019, 11:17:19 AM): Page 3 shows the input wiring for the UPS.
Dan (5/14/2019, 11:17:34 AM): N can also be used as L2
Dan (5/14/2019, 11:17:55 AM): Just wire it like shown and you will be fine
Me (5/14/2019, 11:19:13 AM): Do i need to get a separate hardwire kit or just use existing panels on the UPS for input?
Dan (5/14/2019, 11:20:08 AM): You can use the existing panel to hardwire the input. No need for a input kit.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

0 Likes
0
2032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

You can do that, but the output will be 2 unbalanced hots and a ground when you switch to battery. You will likely track the input when you are in online mode, but then revert to H/H/G on battery. This UPS is not designed for a H/N/G configuration. It is sold in North America and designed for H/H/G. The “XLI” version would be for H/N/G configurations.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

0 Likes
0
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:15 AM . Last Modified: ‎2024-03-15 06:00 AM

Hi Jay 

Just to add to this conversation, as this would be for use in India, I would recommend purchasing the SURT15K solution that is specifically for the India market.  It does appear to be very similar to the XLI version although does not include batteries, but in terms of warranty and after sales support, it would make things less complicated.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore