Turn off UPS after graceful shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Turn off UPS after graceful shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

0 Likes
1
1898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

Turn off UPS after graceful shutdown

Hello,

I don't find the UPS is completely power off with the power LEDs everything off, after the graceful shutdown was done on the servers. Is this the case?  But the logs on the NMC shows this message that the output power is turned off. Does this mean that the power on the UPS is off and no longer draining any battery power? Thank you.

11/08/2014 08:17:33 UPS: The output power is now turned on. 
11/08/2014 08:17:28 UPS: The output power is turned off.   11/08/2014 08:15:56 UPS: Started a reboot process. 
11/08/2014 08:08:42 UPS: A graceful shutdown process is being used to shut down the load equipment before the UPS turns off. Initiated by PowerChute ns from 172.xxx.xxx.xxx.

Regards, Daryl

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

0 Likes
0
1896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

Daryl,

The UPS is not completely of if the NMC is still accessible and if the LCD screen is still active. In general what happens is when PowerChute commands the UPS down the output power will be cut to the attached load and the UPS will enter sleep mode. IN sleep mode the UPS the UPS will continue to power the NMC. You can tell the UPS is in sleep mode when the LEDs on the unit are flashing in sequence / 1 after the other. This will last for around 9 minutes and then the UPS will power down completely to save the battery / batteries. In this state the NMC is not accessible and the LEDs are off.

Example with PowerChute Network Shutdown and SMX1500, PowerChute has been configured to start OS shutdown after UPS on battery for 60 seconds (shutdown delay) and to send power off command to UPS. The UPS outlet groups are configured with a 240 second power down delay.

1 - UPS goes on battery

2 - shutdown delay passes (60 seconds) OS is commanded down

3a - 70 second delay is started (this is built in and not configurable)

3b - Outlet group count down to shutdown starts (power down delay)

4 - OS shutdown starts

5 - OS powers down

6 - Outlet group delay elapses (240 seconds) and power is cut to the outlets

7 - UPS enters sleep mode (LED flash and the NMC is still accessible)

8 - UPS powers down after being in sleep mode for 9 minutes (LED go out and NMC is not accessible)


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

0 Likes
0
1897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:53 AM . Last Modified: ‎2024-03-12 01:34 AM

Daryl,

The UPS is not completely of if the NMC is still accessible and if the LCD screen is still active. In general what happens is when PowerChute commands the UPS down the output power will be cut to the attached load and the UPS will enter sleep mode. IN sleep mode the UPS the UPS will continue to power the NMC. You can tell the UPS is in sleep mode when the LEDs on the unit are flashing in sequence / 1 after the other. This will last for around 9 minutes and then the UPS will power down completely to save the battery / batteries. In this state the NMC is not accessible and the LEDs are off.

Example with PowerChute Network Shutdown and SMX1500, PowerChute has been configured to start OS shutdown after UPS on battery for 60 seconds (shutdown delay) and to send power off command to UPS. The UPS outlet groups are configured with a 240 second power down delay.

1 - UPS goes on battery

2 - shutdown delay passes (60 seconds) OS is commanded down

3a - 70 second delay is started (this is built in and not configurable)

3b - Outlet group count down to shutdown starts (power down delay)

4 - OS shutdown starts

5 - OS powers down

6 - Outlet group delay elapses (240 seconds) and power is cut to the outlets

7 - UPS enters sleep mode (LED flash and the NMC is still accessible)

8 - UPS powers down after being in sleep mode for 9 minutes (LED go out and NMC is not accessible)


Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore