Hi and I hope someone can provide me with some tips on how to proceed:
I am trying to reset the battery constant for my 1999 vintage SU2200NET. I contacted APC tech support via a "chat" instance and was provide the value of hex "AF" as the constant for this UPS.
Using the correct serial cable, I "hyperterm'd" into the unit as follows:
1. Shift-Y. UPS responded with "SM".
2. 0 (zero). UPS responded with "8D". This is the current value of the battery constant.
3. Attempted to change the value using the + (plus) and - (minus) keys.
note: Instead of incrementing or decrementing the value, each time I pressed the key I received the "NO".
4. Shift-R. UPS responded with "BYE".
Does anyone know what the response "NO" means and if there is any way to cause EEPROM/NVRAM to begin to accept the requested change to the battery constant?
I also have an AP9630 (which WAS NOT installed while talking to the UPS via the serial port) but I don't think there is any way to change the battery constant via the NMC.
Any help would be greatly appreciated!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-29 11:38 PM . Last Modified: β2024-03-11 04:41 AM
i think you're missing a step. here are the instructions i have. try this in place of your step 2. press 1 and then about 4 seconds later, press 1 again (should get "PROG"). THEN press 0 and record the value.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-29 11:38 PM . Last Modified: β2024-03-11 04:41 AM
Right you are! I suspected it was a "cockpit" issue. I'll redo it and let you know.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-29 11:38 PM . Last Modified: β2024-03-11 04:41 AM
π
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-29 11:38 PM . Last Modified: β2024-03-11 04:41 AM
I sure am glad we have you here to shepherd us along toward APC nirvana!
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-29 11:38 PM . Last Modified: β2024-03-11 04:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-29 11:38 PM . Last Modified: β2024-03-11 04:40 AM
Hello Angela,
I am hoping you can help with this one too. I have a very old SMART-UPS 1250 and just replaced the batteries in it. The run time of 23 minutes did not change after replacement and seems low to me. I am trying to reset the battery constant but it seems this model is even older and does not respond to the 1 1 command to enter prog mode.
I opened hyperterminal.
Sent Y
Received SM
Sent 0 (zero)
Received 4E
Pressed 1 1 (tried numerous times.)
Received nothing at all.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-29 11:38 PM . Last Modified: β2024-03-11 04:40 AM
If the UPS predicts 23 minutes of runtime, then you can do a runtime calibration, either via PowerChute or a network management card.
Link copied. Please paste this link to share this article on your social media post.