APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-30 05:28 AM . Last Modified: 2024-03-08 02:30 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:28 AM . Last Modified: 2024-03-08 02:30 AM
I have inherited a Smart-UPS 2000. ~2yrs ago, when last plugged in, it was working. Now, when I plug it in and try to start it up, absolutely nothing happens. Unfortunately, I did not inherit the manual and so I have no troubleshooting information. Tried to find a manual on-line, no luck. Can someone tell me how to determine whether or not this UPS unit is ultimately useable or destined for landfill. I don't want to do the latter and would be willing to buy new batteries if that is what is needed. But, I hesitate to do that without some confidence that 'dead batteries' may be the only problem with this system.
Thanks for any help that anyone can provide. Fred P
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:29 AM . Last Modified: 2024-03-08 02:30 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:29 AM . Last Modified: 2024-03-08 02:30 AM
From what you describe, it sounds like you stored it unplugged for a long time. The type of batteries used in most UPSs is called lead acid. They lose the charge with time with the rate of loss being greater at higher temperature.
When you let them sit around and allow them to discharge too much, they're permanently damaged and you must replace them. If you don't see at least 50v at the battery terminals, consider them dead.
Lead price has gone up like copper, so batteries are considerably more costly now than a few years ago. Don't buy batteries until you actually need to use the UPS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:29 AM . Last Modified: 2024-03-08 02:30 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:29 AM . Last Modified: 2024-03-08 02:30 AM
User manual available here:
http://www.refurbups.com/Knowledge-Base/APC-Smart-UPS-Manual
The 2000 needs batteries to start. Using a voltmeter check for 48 to 52 volts at the battery box connector. If very low or no voltage you to need to replace the batteries. The SU2000 is a robust high quality ups and is worth fixing up.
Hope this helps
Scucci
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:29 AM . Last Modified: 2024-03-08 02:30 AM
What is the exact model on it? It should be on the white sticker on the unit some place. It could be just Smart UPS 2000 or AP2000.
The above poster is correct. This will need some good batteries in order to start. If you remove the batteries and then put them back in again (once the UPS is discharged) and try to start the UPS you may get a brief noise the first time and then nothing afterwards. This is also true with the "SU" models i.e. SU2200. The newer SUA models will flash the replace battery light but start up.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:29 AM . Last Modified: 2024-03-08 02:30 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:29 AM . Last Modified: 2024-03-08 02:30 AM
From what you describe, it sounds like you stored it unplugged for a long time. The type of batteries used in most UPSs is called lead acid. They lose the charge with time with the rate of loss being greater at higher temperature.
When you let them sit around and allow them to discharge too much, they're permanently damaged and you must replace them. If you don't see at least 50v at the battery terminals, consider them dead.
Lead price has gone up like copper, so batteries are considerably more costly now than a few years ago. Don't buy batteries until you actually need to use the UPS.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of