This Is Killing Me --> UPS log not in sync with what actually happened.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • This Is Killing Me --> UPS log not in sync with what actually happened.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:25 AM

0 Likes
4
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:25 AM

This Is Killing Me --> UPS log not in sync with what actually happened.

Basically, we had a power outage, the UPS went to battery backup, the UPS battery depleted (or came close), and when power was restored the UPS turned off and stayed off. However, the log is showing that it turned back on and re-established communications. Yet, I had to flip Q3 to put it in bypass and then back off of manual bypass for it to boot up..

I have a Symmetra 40K, this happened the last time too, but no changes have been made to the config (that I know of.) Here's the high points of the log, can someone please shed a little light?

11/15/2009 15:56:18 UPS: Communications established.
11/15/2009 15:56:05 System: Network service started. System IP is 192.168.26.89 from manually configured settings.
11/15/2009 15:56:05 System: Coldstart.
11/15/2009 15:03:54 UPS: Returned from sleep mode.
11/15/2009 15:01:01 UPS: Entered sleep mode.
11/15/2009 15:01:00 UPS: Communications established.
11/15/2009 15:00:47 System: Network service started. System IP is 192.168.26.89 from manually configured settings.
11/15/2009 15:00:47 System: Warmstart.
11/15/2009 14:48:54 UPS: Turned off.
11/15/2009 14:48:54 UPS: Returned from a Low-Battery condition.
11/15/2009 14:48:53 UPS: Bypass not in range cleared; either frequency or voltage.
11/15/2009 14:48:34 UPS: Started reboot sequence.
11/15/2009 14:46:58 UPS: Graceful shutdown by PowerChute ns from 192.168.26.5.
11/15/2009 14:46:57 UPS: Battery power is low and will soon be exhausted.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:24 AM

0 Likes
0
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:24 AM

I didn't get the complete answer, but I'm going to post a broader question after some research. I'm having major issues with getting this to work and I don't know why yet.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:24 AM

0 Likes
0
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:24 AM

I have switched the location of this thread to the "Data Center and Facility UPS" section, as your unit falls under this category. I will check with our 3ph representatives in regards to your concerns.

In the meantime, can you please provide a screenshot of the following items:

The UPS tab -> Shutdown options in the network card of the UPS. (Low battery duration signal, sleep delay, ALL the settings please, etc.)

The UPS -> PowerChute information.

A screenshot of the event configuration in PCNS, as I see you have a PCNS client involved in this shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:24 AM

0 Likes
0
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:24 AM

This appears to be a normal shutdown initiated by PCNS.
The UPS and Web/SNMP card came back on-line as they should have when the power was retored. The UPS will not connect the load until commanded to do so.
Hard switching the bypass powers the load, which the UPS sees then maintains.

This situation usually requires that the UPS is commanded to power the load from the PowerView on the front door or via the Web interface.

Reply

Link copied. Please paste this link to share this article on your social media post.

Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:24 AM

0 Likes
0
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:24 AM

Cool, thanks for the info. I'm still working on getting the screenshots on but I've been slammed.

Is this a setting that may have been changed inadvertently on the UPS? We'd certainly prefer it reboot once power is restored. It seems odd that it worked for years and then randomly stopped rebooting once power returned.

The big problem is that once it depletes we need someone to physically drive to the location to power it on, which isn't close to anything. Ideally it would just boot back up and go back to normal.

Reply

Link copied. Please paste this link to share this article on your social media post.

Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:24 AM

0 Likes
0
1315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:36 AM . Last Modified: ‎2024-03-19 01:24 AM

I didn't get the complete answer, but I'm going to post a broader question after some research. I'm having major issues with getting this to work and I don't know why yet.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of