Thermal emergency shutdown in SMC1000I / SMT1000I - is it supported and how does it work?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Thermal emergency shutdown in SMC1000I / SMT1000I - is it supported and how does it work?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
progmars_apc
Ensign progmars_apc
Ensign

Posted: ‎2021-06-28 09:25 AM . Last Modified: ‎2024-03-17 11:18 PM

0 Likes
3
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:25 AM . Last Modified: ‎2024-03-17 11:18 PM

Thermal emergency shutdown in SMC1000I / SMT1000I - is it supported and how does it work?

I just saw this video which raises some safety questions:

https://youtu.be/dQYT3pCEg5Q?t=127

Indeed - how didn't his SMT turn off when the temperature of the batteries rose so high that they bulged that huge?

I see the following text in descriptions of SMC1000 and SMT1000:

"Temperature-compensated battery charging. Prolongs battery life by regulating the charge voltage according to battery temperature."

But in this case it's not about charging nor about quality of the batteries (he was using the original ones, just 2 years old). It's about thermal shutdown.

How to prevent this from happening? Do I have to somehow activate and tune the thermal shutdown function? Is it at all supported on these two UPS models and will it work also when the UPS doesn't have any computer running PowerChute?

I'm just afraid to imagine what might happen when I'm away from apartment for a few hours. I guess, I'll have to fully disconnect the UPS from the mains power when I'm not at home or even at nights. I've heard that it might be not healthy for batteries when the UPS is turned off for prolonged periods of time, but better safe then sorry.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
progmars_apc
Ensign progmars_apc
Ensign

Posted: ‎2021-06-28 09:25 AM . Last Modified: ‎2024-03-17 11:18 PM

0 Likes
0
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:25 AM . Last Modified: ‎2024-03-17 11:18 PM

I just talked to some guys who seem to have experience with batteries and they explained that unfortunately bulging may occur also very close to room temperature. So, unfortunately thermal shutdown wouldn't help. Maybe only some kind of a smoke detector would work.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:25 AM . Last Modified: ‎2024-03-17 11:18 PM

0 Likes
0
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:25 AM . Last Modified: ‎2024-03-17 11:18 PM

Hi Martin,

There are a few unknowns in the video (in what conditions have the batteries been stored or how they were used), but APC UPS units have a number of thermal protection features that do decrease the likelihood of these types of events occurring. For example, on the battery side, a thermal switch closes, and the charger is shut off, once the internal high temperature threshold is reached. Or, the UPS output is turned off, once the internal heatsink temperature sensor exceeds its high temperature threshold. 

These are built in safety features that do not require management options like Powerchute. Powerchute would enable additional options like graceful shutdown based on ambient temperature (used in conjunction with network management card and temperature sensor). 

Smart-UPS battery chargers are smart too, and they work at regulated capacity, as required by the battery. If the UPS is off, or in standby, and the batteries are fully charged, the charger will turn off too.

Reply

Link copied. Please paste this link to share this article on your social media post.

progmars_apc
Ensign progmars_apc
Ensign

Posted: ‎2021-06-28 09:25 AM . Last Modified: ‎2024-03-17 11:18 PM

0 Likes
0
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:25 AM . Last Modified: ‎2024-03-17 11:18 PM

Thanks for the explanation.

Well, it seems in this case (and I've heard many similar stories about bulged batteries) thermal protection did not work and I do not understand why. It doesn't matter if the batteries are good or bad or dying - if they start bulging and smoking, it means the temperature was going up rapidly and the sensor should have shut down the charger (or better - the UPS) immediately.

So, do I understand correctly that it's impossible to use internal thermal sensor alone to configure thermal shutdown in Powerchute and I would need an external sensor? That's sad and it wouldn't work for SMC because it has no slot for management cards.

I guess, I'll have to buy some other thermal solution with alarm. I could even create it myself out of simple Arduino board, speaker and thermosensor.

Still, it makes me sad that I have to append some artificial solutions to an expensive Smart UPS (400 - 500 EUR which is half of my equipment cost) just to make it safe to use. Thermal shutdown shouldn't be an advanced external accessory; it should be a basic safety feature. If the device heats up enormously above expected range, turn the UPS off completely and don't charge it anymore until user investigates the situation and decides if it's ok to restart the UPS. Simple and straight forward, especially for a device that has "smart" in its name.

Reply

Link copied. Please paste this link to share this article on your social media post.

progmars_apc
Ensign progmars_apc
Ensign

Posted: ‎2021-06-28 09:25 AM . Last Modified: ‎2024-03-17 11:18 PM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:25 AM . Last Modified: ‎2024-03-17 11:18 PM

I just talked to some guys who seem to have experience with batteries and they explained that unfortunately bulging may occur also very close to room temperature. So, unfortunately thermal shutdown wouldn't help. Maybe only some kind of a smoke detector would work.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore