Thermal/Humidity Sensors - What's the difference between MIN/LOW/HIGH/MAX?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Thermal/Humidity Sensors - What's the difference between MIN/LOW/HIGH/MAX?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:26 PM . Last Modified: ‎2024-03-06 03:11 AM

0 Likes
1
1161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:26 PM . Last Modified: ‎2024-03-06 03:11 AM

Thermal/Humidity Sensors - What's the difference between MIN/LOW/HIGH/MAX?

We are using the Powerchute Network Shutdown with the network management cards with Environmental monitoring, specifically thermal and humidity.

We simply would like the system to notify us(via email) when it gets to 35 degrees, and then shutdown automatically if it hits 45 degrees. This would give us time to respond to a faulty air conditioning unit etc..

Everything is working well for the shutdown scripts, but we can't seem to trigger an email for any of the thresholds other than MIN/MAX. The problem is not the smtp settings or anything, it's that the Network Client system doesn't seem to allow us to react to a LOW/HIGH temperature threshold, only MIN/MAX.

Question: We can see the varying thresholds, but how can we setup actions for each of them(other than just min/max), monitoring from the central Network client?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • action
  • email
  • environmental
  • network
  • shutdown
  • threshold
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:27 PM . Last Modified: ‎2024-03-06 03:10 AM

0 Likes
0
1161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:27 PM . Last Modified: ‎2024-03-06 03:10 AM

powerchute network shutdown can only shut down based on ANY violation. you cannot really specify unfortunately.

but before i figure something out here to see if we can workaround it to do what you want, can you provide me the config.ini and event.txt from your network management card for review. refer to [these instructions|http://nam-en.apc.com/app/answers/detail/a_id/9321] to download the files.

thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:27 PM . Last Modified: ‎2024-03-06 03:10 AM

0 Likes
0
1162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:27 PM . Last Modified: ‎2024-03-06 03:10 AM

powerchute network shutdown can only shut down based on ANY violation. you cannot really specify unfortunately.

but before i figure something out here to see if we can workaround it to do what you want, can you provide me the config.ini and event.txt from your network management card for review. refer to [these instructions|http://nam-en.apc.com/app/answers/detail/a_id/9321] to download the files.

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore