The compressor of an ACSC100 does not cycle on and off, only stays "on"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The compressor of an ACSC100 does not cycle on and off, only stays "on"
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-18 11:28 PM

0 Likes
3
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-18 11:28 PM

The compressor of an ACSC100 does not cycle on and off, only stays "on"

We have an ACSC100 unit, "Spot" type configuration, has been alarmed by: "Rack inlet high temperature violation", "high discharge pressure alarm", "persistent high discharge pressure alarm" and "supply air high temperature violation" and the equipment stays in "Idle" condition. We reset the equipment and it works, Pressures: Suction: 154 PSI, discharge: 389 PSI, and the compressor don't off, does not cycle on and off. This condition is maintained until the Inrow returns to "idle" condition.

The rack inlet temperature sensor it works normally also the mechanical part of the equipment (compressor, pipes, etc) appears to be fine. The Heat load of the room is an APC PDU with transformers.

What could be the cause of the problem, the control card? 

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-18 11:28 PM

0 Likes
0
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-18 11:28 PM

Hello Ivan.

If the compressor is staying on with the unit in standby, check the compressor relay. It may be getting stuck closed. There is 208 volts going to the relay so a qualified HVAC tech will need to check the relay. 

Thank you

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-18 11:28 PM

0 Likes
0
783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-18 11:28 PM

Hello Ivan.

How long does the unit run for before it goes into high discharge pressure alarm? What does the discharge pressure go to right before it goes into high discharge pressure alarm? What is the cooling demand show on the unit while it is running?

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-18 11:28 PM

0 Likes
0
783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-18 11:28 PM

Hi, the unit began to go to the high discharge pressure alarm every 5 or 4 hours. the cool demand was between 3 to 4.8 kw but the compressor did'nt stop. On sunday we changed the control board from the user interface box from another same model Inrow and the equipment works normally performing the normal compressor "on and off" cycle. But today appears this problem: the equipment goes to idle condition again by high discharge pressure, appears this alarm: "startup line pressure imbalance alarm" and the discharge pressure goes to 540 PSI meanwhile the suction pressure is: 164 PSI. We adjust the pressures, we discovered that a pressure sensor from the suction line was incorrectly placed (did'nt make contact) and we repaired it, the equipment works but when we turn it off and start again , it goes to idle condition because the discharge pressure goes high again. We turn it off the equipment and when start again the compressor turns on even the equipment is on stand by condition.

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-18 11:28 PM

0 Likes
0
783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-18 11:28 PM

Hello Ivan.

If the compressor is staying on with the unit in standby, check the compressor relay. It may be getting stuck closed. There is 208 volts going to the relay so a qualified HVAC tech will need to check the relay. 

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of