Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Error Report APC InRow Unit
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2801:29 AM. Last Modified: 2024-03-1811:28 PM
Hello Jorge.
The relay output is just an relay that changes state when an alarm is on the unit. I am not worried about that alarm. The Fan Power Supply left fault alarm is the one to look at. This is saying the left fan power supply is in fault. The best thing to do is to pull out the two power supplies and then swap the left and the right supply. See if the fault follows the supply or stay with the bay. If the alarm clears then the power supplies just needed to be reseated. If the fault follows the supply then that power supply will need to be replaced. If it stays with the bay (left) then please call into your local tech support and they will be able to assist further.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2801:29 AM. Last Modified: 2024-03-1811:28 PM
Hello Jorge.
The relay output is just an relay that changes state when an alarm is on the unit. I am not worried about that alarm. The Fan Power Supply left fault alarm is the one to look at. This is saying the left fan power supply is in fault. The best thing to do is to pull out the two power supplies and then swap the left and the right supply. See if the fault follows the supply or stay with the bay. If the alarm clears then the power supplies just needed to be reseated. If the fault follows the supply then that power supply will need to be replaced. If it stays with the bay (left) then please call into your local tech support and they will be able to assist further.
Thank you