The best way to simulate a power failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The best way to simulate a power failure
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

0 Likes
3
2226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

The best way to simulate a power failure

Hi, we had 3 batteries fail in our Symmetra unit a few days ago, after an outage. Ejecting them and putting them back in fixed them.


We do want to simulate a power failure, just to see how true the 1hr 55min runtime is on the display.

Is the best way to do a 30-60 min test to just flip the input circuit breakers to off? and then back on again once we want to put power thru to the UPS?

Our UPS is hardwired into the wall, and we would have to access the building power area to actually turn off the switch (which we dont have access to directly).

Thanks,
Dekkar

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:12 AM

0 Likes
0
2224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:12 AM

Hi guys, they failed again.


I did flick the input circuit breaker switches (in a very nervous state) and the UPS just switched onto battery mode..


The 1:55 hrs went down to about 60 mins in the first 30 mins...... and then kind of steadied out, I presume that in the first 30 mins the batteries failed etc etc which resulted in reduced runtime.

I'll arrange to get the faulty batteries replaced. We had them all replaced around 2 years ago.


Thanks,
Dekkar

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

0 Likes
0
2224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:13 AM

Your Symmetra detected the bad battery modules when it tried to use them during your power failure. Ejecting and re-inserting them causes the Symmetra to think they're new (or at least different) battery modules. It will probably re-detect them as bad when you do the power failure test.

If you bought all of your battery packs at the same time, it is quite likely that the other modules are of an age where they should be replaced as well because they may start failing soon. You can check the serial numbers on all the battery modules to see if they start with the same 4 or 5 characters, or post them here and someone from APC may be able to look them up - I'm just another end user. I have a Symmetra with 12 SYBT2's and after replacing all of the batteries around 4 years ago, they are now starting to report failures. It started a few months ago, and I pulled those modules out. Some more failed, and I pulled those out, and so on. I'm down to 6 modules now and have new batteries for all 12 on order.

One way to detect some (but not all) pre-failing battery modules is to touch the outside of the module (not by the connector, of course!) and see if it feels hot to the touch.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:12 AM

0 Likes
0
2224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:12 AM

yes, i agree with terry. generally reseating batteries that 2-5 years old is not a good idea cause they will just fail again during a UPS self test. you should check the age and it is likely if they are all the same age, that they all actually failed or are of reduced capacity.

you'd probably want to check into replacing all of them if they are 2-5 years old instead of discharging them and potentially wasting the capacity they have left while you are pursing new batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:12 AM

0 Likes
0
2225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-13 01:12 AM

Hi guys, they failed again.


I did flick the input circuit breaker switches (in a very nervous state) and the UPS just switched onto battery mode..


The 1:55 hrs went down to about 60 mins in the first 30 mins...... and then kind of steadied out, I presume that in the first 30 mins the batteries failed etc etc which resulted in reduced runtime.

I'll arrange to get the faulty batteries replaced. We had them all replaced around 2 years ago.


Thanks,
Dekkar

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of