The battery power is too low to support the load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The battery power is too low to support the load
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

0 Likes
5
4559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

The battery power is too low to support the load

I'm getting repeated alerts that read "Critical - UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately," referencing error code 0x0107, followed almost immediately by a message saying "Informational - UPS: A discharged battery condition no longer exists," referencing error code 0x0108. These messages come in groups of 2-10, every few hours.  When I log into the network card, it shows no alarms present, capacity of 98%, and 6 minutes of run time.  The battery was replaced (OEM) 10 months ago.

A search of these forums yielded this: http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/10730/discharged-battery-bug-...

The description of the problem in the above link is almost identical to what I'm seeing, but apparently there is some undocumented way to reset a battery constant.  Does anyone have further information on resolving this error?  Do I just need to replace the battery again already?

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

0 Likes
0
4558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

And depending on if you have APC batteries or some equivalent, the equivalents may not pass calibration correctly.  I had a 1000va unit with a BTI battery that has never passed calibration, but would still support the load, but would never have a proper runtime listed.  The battery finally died and put in an APC battery and all is much better.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

0 Likes
0
4558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

Hi Andy,

What's the model of your UPS?

Those messages occur when the runtime on battery drops below the "low battery duration" setting. It sounds like every few hours the load increases causing runtime to drop below the setting. Considerations then are:

- Is the estimated runtime accurate now that you've replaced the battery? You can look at the expected runtime charts for your UPS on APC's website. If the estimate is off, then doing a "runtime calibration" should help the UPS update its estimate. Runtime calibration requires load on the UPS to be at least 30% and non-varying -- some good loads could be light bulbs or hair dryers. It can be commanded via PowerChute or the Network Management Card, or by just unplugging the UPS and let it run on battery until it shuts down.

- If the runtime is accurate, does the "low battery duration" reflect the true amount of time + safety margin the attached loads need to safely shut down? By default this setting is 2 minutes but perhaps it has been changed. If the setting is excessively generous, you could decrease it.

- If the runtime is accurate and the low battery duration is correct, then perhaps the UPS doesn't have enough runtime for the loads. Some UPSes can accept additional battery packs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

0 Likes
0
4558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

The UPS in question is a Smart-UPS 2200 RM.

There's already a very low load on this device, so I would think it would have to be a massive spike in order to cause the runtime to drop. I'm going to attach a screenshot of the UPS status screen.  I have 4 more similar UPS's, and 3 of the 4 have more load (in Watts), and none of them are having this problem.  They all show runtimes in the 25-37 minute range.

If I'm properly interpreting the chart I find at http://www.apc.com/products/runtime_for_extendedruntime.cfm?upsfamily=165, then my UPS should have ~40 minutes of runtime at a 19% load, but mine is showing 6 minutes.  Could this mean I have a bad battery, or that I need to calibrate it?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

0 Likes
0
4558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

It sounds like the UPS doesn't have enough load to do a runtime calibration. Chances are good that the runtime estimate hasn't been updated since using the old battery. The UPS needs a constant load of at least 30% for calibration to succeed.

APC is a little confusing in that the have the name of the UPS "Smart-UPS 2200 RM" which can refer to different models, such as "SMT2200RM2U". The model is usually listed on a white sticker.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

0 Likes
0
4558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

Thanks for the information!  I'm going to read up on performing a calibration.

Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

0 Likes
0
4559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:24 AM

And depending on if you have APC batteries or some equivalent, the equivalents may not pass calibration correctly.  I had a 1000va unit with a BTI battery that has never passed calibration, but would still support the load, but would never have a proper runtime listed.  The battery finally died and put in an APC battery and all is much better.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of