The art of hysteresis adjustment
  • The art of hysteresis adjustment
Posted: ‎2021-06-28 09:48 PM . Last Modified: ‎2024-03-14 11:36 PM
1587
We had a bit of an issue over the weekend - our pagers were spammed fairly heavily by a sensative temperature probe. We would receive an alert when the probe hit 73 degrees farenheit - and then a subsequent clear, and then an alert, and then a clear, etc, etc. 106 times in 8 minutes.
Is it the hysteresis setting that would resolve this? Setting the hysteresis to 2 degrees variance? (it's currently set to 0)
Any help would be most appreciated.
Thanks!
Drew
Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander
Posted: ‎2021-06-28 09:48 PM . Last Modified: ‎2024-03-14 11:35 PM
Just an additional tip -
Make sure you do not set hysteresis too high, or else you can run into a situation where it isn't feasible to actually clear an alarm. It all really depends on your high thresholds and the sensitivity that you wish to be alerted on.
Erasmus_apc
Sisko Erasmus_apc
Sisko
Having the hysteresis set to 0 degrees is the issue. The alarm is triggering and since there is no "delta" or difference required for it to clear, it just clears and re-triggers over and over. As you have asked, a 2 deg. hysteresis should cut down on your alarms. The size of the hysteresis setting is somewhat up to your own knowledge of the room/rack environment and your tolerance for alarms. Some customers are fine with a very low setting, others use 5 or 6 degrees.
Great - thanks Erasmus
Cap1_apc
Lt. Commander