System: Detected an unauthorized user attempting to access the SNMP interface

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • System: Detected an unauthorized user attempting to access the SNMP interface
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:10 AM . Last Modified: ‎2024-03-05 10:23 PM

0 Likes
7
3771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:10 AM . Last Modified: ‎2024-03-05 10:23 PM

System: Detected an unauthorized user attempting to access the SNMP interface

Dear all,

My company has one UPS model Smart-UPS RT 10000 RM XL and use Network Managerment Card to control and monitor it.

Everything work fine and i can receive the report or notification about UPS when it got issue (like no power, selftest, ...). But sometime i get many emails with detail like that:

System: Detected an unauthorized user attempting to access the SNMP interface ........

First, I find in Webportal of UPS the logs and found this issue happen by 3 IP below:

- 196.34.139.65 (with this IP, i really don't know this ip assign for which device).

- 10.73.15.108 -> PC to monitor all device (HP Printer, UPS, ...). On this computer, i install HP Webjet admin to monitor HP Printer.

- 10.73.5.177 -> The old printer server

The second step i find the reason why 3 PC looking for something in this UPS.

On the PC install HP Webjet Admin, i start discovery new device on network. After that, UPS start send email for me, too.


1348_UPS Report.jpg

Please tell me how can i disable this reports or the way to resolve this issue. Thank you !


Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

0 Likes
0
3768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

It looks like SNMP probing is key to Jetadmin's device discovery process:

HP Web Jetadmin Software - Device Discovery FAQ - c01718860 - HP Business Support Center

so disabling the alert seems to be the way to go.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

0 Likes
0
3768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

Yes, I believe so!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

0 Likes
0
3768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

Dear Angela N

I setting in Administration > Network > SNMP like this

1368_2.jpg

But after save this setting, i still get the email report like this:

1369_1.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

0 Likes
0
3768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

Are the more recent email notifications at the top or bottom? I see the alerts where you edited the address and community so I am going to assume the more recent events are at the top (from the one from 10.73.5.177).

If this is not working, you'll need to review the other options we've outlined. cry

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

0 Likes
0
3768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

Hi,

Every time I change the SNMP setting, i alway receive 2 email alert about it. Then, there are many emails come from another IP. And it is continuous smile,

At this moment, i changed my setting to default setting and accept sometime i receive email alarm about System: Deteced an unauthorized user attemping to access the SNMP interface.

Maybe, i will remove this alarm from setting but i need to my manager accept that.


Thank you for your support !

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

0 Likes
0
3768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

Dear all,

My company has one UPS model Smart-UPS RT 10000 RM XL and use Network Managerment Card to control and monitor it.

Everything work fine and i can receive the report or notification about UPS when it got issue (like no power, selftest, ...). But sometime i get many emails with detail like that:

System: Detected an unauthorized user attempting to access the SNMP interface ........

First, I find in Webportal of UPS the logs and found this issue happen by 3 IP below:

- 196.34.139.65 (with this IP, i really don't know this ip assign for which device).

- 10.73.15.108 -> PC to monitor all device (HP Printer, UPS, ...). On this computer, i install HP Webjet admin to monitor HP Printer.

- 10.73.5.177 -> The old printer server

The second step i find the reason why 3 PC looking for something in this UPS.

On the PC install HP Webjet Admin, i start discovery new device on network. After that, UPS start send email for me, too.


1348_UPS Report.jpg

Please tell me how can i disable this reports or the way to resolve this issue. Thank you !


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

0 Likes
0
3768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

These three IP addresses apparently have SNMP capability so you'd have to research in order to how to disable it on those particular devices. Or maybe they have a program installed doing it. They must be periodically doing scans or SNMP requests periodically somehow.

Before disabling the notification, you could change the NMS IP/Hostname settings on your SNMP configuration so that it does not allow every IP address (assuming it is at default) to try and access the device. See my screenshot below (assuming you have the same firmware as me - if you don't let me know). You can read the help file on how to configure this screen (click help on the top right next to log off for context sensitive help) and lock down your SNMP settings.

1355_snmp.jpg

Keep in mind disabling the notification won't solve the issue and more just cover it up. I'd definitely research what is going on with those three machines in an attempt in stopping the SNMP scan traffic since if these devices continue doing it frequently, it could cause performance issues with the Network Management Card in some instances if it keeps getting unnecessary SNMP traffic very frequently. Alternatively like I said, change around your SNMP settings on the management card per the help file.

If you want to disable the alert while you are researching the issue, you can disable it. I will assume you have the older v3.X.X or v5.1.X firmware depending on your model of network management card. Assuming this, you could go to Administration->Notification->By Event->System Events and look on the list for this event.

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

0 Likes
0
3769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:11 AM . Last Modified: ‎2024-03-05 10:23 PM

It looks like SNMP probing is key to Jetadmin's device discovery process:

HP Web Jetadmin Software - Device Discovery FAQ - c01718860 - HP Business Support Center

so disabling the alert seems to be the way to go.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore