Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

System: Detected an unauthorized user attempting to access the SNMP interfa

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • System: Detected an unauthorized user attempting to access the SNMP interfa
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
9
3634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

System: Detected an unauthorized user attempting to access the SNMP interfa

Greetings,

I've seen a number of posts on this topic but have not seen a response that fixes my problem. Since having installed PowerChute Network Shutdown on my server, I am receiving this alert from the two UPS's that I have configured in the software. I receive 8 alerts from each UPS at 2:00 AM, 9:00 AM, 4:00 PM and 11:00 PM.

Name : UPSSERVER2
Location :
Contact :
http://UPSSERVER2.
http://192.168.100.4

Serial # :
Device Ser #:
Date: 09/02/2010
Time: 08:03:02
Code: 0x0004

Informational - System: Detected an unauthorized user attempting to access the SNMP interface from 192.168.100.10.

192.168.100.10 is the Windows 2003 server on which the PCNS utility is installed.

PowerChute Network Shutdown 2.2.4 for Microsoft® Windows®. Build 954

I have disabled SNMP from the HP printer driver that is installed on the server.

This is a file and print server so there is no other network monitoring software running on it that would explain this.

I don't see anywhere in the PCNS utility to even configure an SNMP string. It only asks for the administrator's userid, password and authentication phrase.


The management card has been upgraded with the latest OS.

Hardware Factory

Model Number: AP9617
Serial Number:
Hardware Revision: A10
Manufacture Date: 05/11/2007
MAC Address:
Management Uptime: 8 Days 20 Hours 29 Minutes


Application Module

Name: sumx
Version: v3.7.2
Date: 02/02/2010
Time: 19:08:16


APC OS (AOS)

Name: aos
Version: v3.7.3
Date: 02/02/2010
Time: 17:05:14


Because I have another UPS on the same network that is not reporting this SNMP attempt, I have got to believe that it is the PCNS utility sending unicast SNMP requests to these two UPS's. How can I configure the proper SNMP string in this utility to make these alerts stop?

TIA

Jeff

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:39 PM

0 Likes
0
3630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:39 PM

Good day Jeff,

Can you download the config.ini, event.txt and data.txt of your NMC and attach it here in the forum and or send it to me thru PM? Also this it what I got from our product specialist. PowerChute Network Shutdown (PCNS) has no SNMP functionality/ libraries on it. By default our NMC has SNMPV1 enabled and it uses community string of public and it uses UDP port 161. PCNS sends UDP packets but it is using port 3052.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
0
3630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

Hello LandLord,

Are you using SNMP on your network or on this UPS? If not, please login to the network management cards web interface and then click on the Administration tab. Then click on Network, from there you'll see SNMPv1 and SNMPv3. Click on access on both of them and if you see a check mark where it says Enable SNMPV1 or SNMPv3 access, click on it to remove the mark and hit on apply. After applying the settings you need to log off and wait for 1-2 minutes for the card to reboot.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
0
3631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

Are you using SNMPv1 or SNMPv3? On the NMC interface whether you choose SNMP1 or 3 there should be a link that would take you on the configuration page for the community string and the NMPS IP/Hostname.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
0
3631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:40 PM

We are using SNMPv1. SNMPv3 is disabled. The NMS can see the UPS just fine. That is not the problem.

The PCNS server is the offending server. I have sniffed the packets and found it to be sending an SNMP query using the community string of 'public' to the UPS's configured when the software was installed.

How does one make the PCNS stop trying to communicate with the UPS's using SNMP and/or how does one change the string it's using?

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:39 PM

0 Likes
0
3631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:39 PM

Let me see if I could find more information about this.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:39 PM

0 Likes
0
3631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:39 PM

Good day Jeff,

Can you download the config.ini, event.txt and data.txt of your NMC and attach it here in the forum and or send it to me thru PM? Also this it what I got from our product specialist. PowerChute Network Shutdown (PCNS) has no SNMP functionality/ libraries on it. By default our NMC has SNMPV1 enabled and it uses community string of public and it uses UDP port 161. PCNS sends UDP packets but it is using port 3052.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:39 PM

0 Likes
0
3630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:54 AM . Last Modified: ‎2024-03-13 11:39 PM

i have never seen this issue just randomly happen. there must be something running on that server, totally unrelated to PCNS, that is trying to do some SNMP GETs/walks or something and keeps hitting the NMC but it is not authorized to do so.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:55 AM . Last Modified: ‎2024-03-13 11:39 PM

0 Likes
0
3630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:55 AM . Last Modified: ‎2024-03-13 11:39 PM

Hi Jeff,

I would like to double check with you. Based from you event log the IP address of the node that tries to access your NMC using SNMP is 192.168.100.10. Is this correct? Is this the IP address of the PC where the PCNS software is installed as well?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:55 AM . Last Modified: ‎2024-03-13 11:39 PM

0 Likes
0
3629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:55 AM . Last Modified: ‎2024-03-13 11:39 PM

i have an idea - since this is happening quite frequently, can you possibly just turn off/stop the APC Powerchute Network Shutdown service via Administrative Tools for 10-15 minutes to see if the messages stop, then don't forget to restart it after your testing. once the service is stopped, if you access PCNS at http://127.0.0.1:6547 or however you access it, it should not respond since the service is stopped. it of course would also say stopped in the services window.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:55 AM . Last Modified: ‎2024-03-13 11:39 PM

0 Likes
0
3629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:55 AM . Last Modified: ‎2024-03-13 11:39 PM

Greetings,

I've seen a number of posts on this topic but have not seen a response that fixes my problem. Since having installed PowerChute Network Shutdown on my server, I am receiving this alert from the two UPS's that I have configured in the software. I receive 8 alerts from each UPS at 2:00 AM, 9:00 AM, 4:00 PM and 11:00 PM.

Name : UPSSERVER2
Location :
Contact :
http://UPSSERVER2.
http://192.168.100.4

Serial # :
Device Ser #:
Date: 09/02/2010
Time: 08:03:02
Code: 0x0004

Informational - System: Detected an unauthorized user attempting to access the SNMP interface from 192.168.100.10.

192.168.100.10 is the Windows 2003 server on which the PCNS utility is installed.

PowerChute Network Shutdown 2.2.4 for Microsoft® Windows®. Build 954

I have disabled SNMP from the HP printer driver that is installed on the server.

This is a file and print server so there is no other network monitoring software running on it that would explain this.

I don't see anywhere in the PCNS utility to even configure an SNMP string. It only asks for the administrator's userid, password and authentication phrase.


The management card has been upgraded with the latest OS.

Hardware Factory

Model Number: AP9617
Serial Number:
Hardware Revision: A10
Manufacture Date: 05/11/2007
MAC Address:
Management Uptime: 8 Days 20 Hours 29 Minutes


Application Module

Name: sumx
Version: v3.7.2
Date: 02/02/2010
Time: 19:08:16


APC OS (AOS)

Name: aos
Version: v3.7.3
Date: 02/02/2010
Time: 17:05:14


Because I have another UPS on the same network that is not reporting this SNMP attempt, I have got to believe that it is the PCNS utility sending unicast SNMP requests to these two UPS's. How can I configure the proper SNMP string in this utility to make these alerts stop?

TIA

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of