We have a fault on our Symmetra VT 30KVA - it throws "System fault detected by surveillance". Documentation says that this is an internal error and to check for other alarms.
The SNMP card no longer detects the UPS - It will report the cards own data (eg temp probe) but "No UPS found". I was hoping to find more information / alarms there. I have tried a different, known working card but with the same results.
I've read the forums and looked through the internet and it seems that more information can be gleaned from the RAW data. I include that here.
M States = 02 04 04
00000000 00000000
00000000 01
Any tips? I'm going to try removing and re-seating the power module now.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 09:29 PM . Last Modified: 2024-01-31 02:55 AM
Decoding RAW status data is not something we can do here unfortunately. We don't have access to the tools. Along with other details, this type of info needs to be analyzed by your local support team in order to determine the state of your UPS. I recommend you email/phone your local support office for the quickest support. Contact info is available here if you need it -> http://www.apc.com/site/support/index.cfm/contact-information/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 09:29 PM . Last Modified: 2024-02-14 02:32 AM
Its been a few days now, do any of the engineers have a suggestion?
Can the raw data be interpreted for me?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-29 09:29 PM . Last Modified: 2024-01-31 02:55 AM
Decoding RAW status data is not something we can do here unfortunately. We don't have access to the tools. Along with other details, this type of info needs to be analyzed by your local support team in order to determine the state of your UPS. I recommend you email/phone your local support office for the quickest support. Contact info is available here if you need it -> http://www.apc.com/site/support/index.cfm/contact-information/
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.