Symmetra RM 6000 Fan Failure Problem

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra RM 6000 Fan Failure Problem
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:12 AM

0 Likes
4
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:12 AM

Symmetra RM 6000 Fan Failure Problem

I have one of my Symmetra RM 6000 UPS's that has encountered a "system level fan failure". I have about 35 of these in service and this is the first time I've encountered this fault. I inspected the unit and found that the main chassis fan on the back of the chassis itself was not running. I ordered a replacement fan through my local APC source and installed the new, identical fan today. The new fan started right up, but the failure alert on my Infrastruxure Manager interface persists, as it does on the unit itself. I tried running a fresh self-test and even tried restarting the management interface, but the failure remains. Is there a fan in the chassis that I can't see (besides those contained in the Power Module) that is the cause of the ongoing failure, or am I missing some other reset mechanism? This unit also utilizes an SYTF2 step-down transformer, but there is no intelligence between the chassis and this unit to my knowledge. Any ideas?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • fan_failure
  • symmetra_rm_6000
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

I appreciate that thought. I just tried it, but still no difference. I'm still waiting for a new MIM to arrive to see if it sees things differently or not. I'll keep waiting....

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

Thank you so much for your response. I am checking with the vendor to see what the part number is that he sent. In the meantime, I will try the other things you suggest and go from there. My first response was to try rebooting the management interface, but that had no impact on the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

I checked with my vendor, and he verifies that that is the part number provided. I went in again, removed the fan, disconnected it, checked all the connections and everything looks fine. The fan is running just fine. I have rebooted the management interface several times, but to no avail. The remaining thing for me to try at this point is to put in another MIM, which I will do soon, as I have a ready spare in transit. After that, I don't know.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

In my experience on some alarms I have to delete the device from Manager and re-add it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

0 Likes
0
1307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

I appreciate that thought. I just tried it, but still no difference. I'm still waiting for a new MIM to arrive to see if it sees things differently or not. I'll keep waiting....

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of